I have a cement block garage that I want to convert into a studio. Is sprayed foam into each block a good choice?

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Emma,
    No, you can't effectively insulate a concrete-block wall by installing insulation in the cores of the block.

    First of all, in a well-built concrete-block (CMU) wall, not all of the cores are empty. Some of the cores should be filled with grout (soupy concrete) and rebar.

    However, the main problem with this approach is that concrete is a good thermal conductor, so you get massive thermal bridging. The heat just follows the obvious path -- through the concrete -- and the flow of heat is barely affected by the small pockets of insulation.

    To insulate this type of wall, you need to install a continuous layer of insulation -- usually rigid foam insulation, although mineral wool panels are another option. The insulation can be installed on the interior or the exterior of the wall -- although installing the insulation on the exterior is almost always preferred, because that approach can address the intersection of the wall and the concrete slab better than the interior approach.

  2. Chaubenee | | #2

    Two inches of taped foam on outside with furring strips to hold the siding every 16oc. is how I would do it.

  3. Expert Member
    Dana Dorsett | | #3

    Sprayed foam never works in CMU cores anyway- they ususally use non-expanding injection foam. While it's R-value is pretty good (R5 per inch), the thermal bridging of the concrete webbing robs it of most of it's performance. A continuous sheet of R6 on the exterior would outperform an injection foam solution in 8" blocks.