Insulation behind a gas fire place?

9yWyBUx7rU | Posted in General Questions on

Have a client that has a high level of air infiltration from behind their gas fireplaces. The house is insulated but behind the fireplaces the brick is exposed and the area along the floor is unsealed.

Can I add ridged foam to the back wall of the fireplace, seal with foam around the edges and then cover with drywall?

Do I need to work about a vapor barrier in this space?

This area seemed to be missed during inspections when the house was renovated and the draft will extinguish a candle outside of the fireplace.

Thanks

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Charles,
    More information, please! Does this fireplace have a traditional brick chimney? Or are you describing some sort of decorative brickwork?

    Is it a gas-fired metal fireplace insert that has been retrofit into a wood hearth? Or some other configuration?

  2. 9yWyBUx7rU | | #2

    Martin thanks for getting back to me

    No brick chimney just a chase that the former builder built out to look like a chimney - the chase is made out of drywall and 2 x 4 framing

    The brick is on the back side of the chase and is the exterior wall of the unit which is no longer attached to another unit as they tore that other unit down and now it is an exterior outside wall not just a party wall

    It is a gas fired insert that has been inserted into a wood frame with marble surround and wood mantel. Walls on both sides of the chase have been insulated and are dry-walled but the space behind the fireplace insert and the floor have never been sealed. This condition is on two floors in the living room and in the master bedroom.

    The chase runs up to the attic - almost like there was a chimney in that space but there are no other signs that it was actually there. The chase therefore works like a chimney and draws nice cold air from the attic down into the house.

    The inserts do have proper vent lines running up to the roof line where they are vented.

    Another thing is that the shut-offs are not accessible and if they were needed to shut the gas you would have to break into the drywall on the side that form the chase.

    Felt we could provide a hatch in the side of the chase to access the shut-offs and at the same time that we opened that area for the hatches we could open the wall enough to insulate and seal behind the fireplace inserts

    Hope this helps - thanks

  3. GBA Editor
    Martin Holladay | | #3

    Charles,
    If exterior brick veneer is exposed behind your metal fireplace, and if there is no insulation on the interior side of the brick veneer, than you obviously have a problem.

    All areas of your home's thermal envelope need insulation and an air barrier. If the builder left out insulation and air barrier details, you have a lot of work facing you.

    You'll have to remove as much of the fireplace as necessary to gain access to the areas that need work. The first step is air sealing, using the usual bag of tricks: spray foam, caulk, panels of plywood, rigid foam, drywall, sheet metal -- different materials for different applications.

    Then you need to install insulation. Consult your local code to determine the minimum insulation thickness for your climate.

    Finally, the interior side of the insulation usually needs to be protected by an air barrier (for example, drywall). It's also important to meet all local requirements for thermal barriers, as well as all clearance requirements for air spaces between wood framing and certain fireplace components.

    If you are unsure of any of these details, consult with your local building official.

  4. jbmoyer | | #4

    Charles,
    I suggest you take a look at the detail found in the Strategies and Details page of GBA (you may have to purchase a GBA membership to view the detail):
    https://www.greenbuildingadvisor.com/cad/detail/air-sealing-platform-manufactured-fireplace-assembly
    -This is what your builder should have done.