Insulating an unvented roof CZ6

dennis_vab | Posted in General Questions on

I have a few bump outs in my home under construction, where I will not be able to have a vented roof.

I would like to avoid using spray foam. What other options do I have in NY state,  climate zone 6? I have 2×8 rafters 24 o.c. I will most likely start by air sealing this area. 

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
    Michael Maines | | #1

    Your only code-compliant, safe option is to insulate the exterior side of the roof, with either rigid foam or a lower-carbon option, with up to 50% (but not more) of the total R-value in the rafters.

    Actually another option would be to over-vent your roof; run 2x furring above the roof sheathing and another layer of sheathing, or cross-strap for a metal roof.

    1. dennis_vab | | #2

      Part of the roof already has shingles on it. Does that leave spray foam as the most viable option?