Insulating a 14-inch I-joist vented cathedral roof in Climate Zone 5

user-5594283 | Posted in Energy Efficiency and Durability on

Hello and thank you for taking the time to answer my question.

I have a Cathedral Roof constructed with 14″ i-Joists in SE BC, Canada.
The Roof Construction from Exterior to Interior follows:

1) Standing Seam 12″ , 24 Gauge Metal Roof
2) Titanium UDL 50 Underlayment
3) PSU 30 Underlayment on along ridge, eaves and rakes
4) 5/8 T&G Plywood
5) Entire roof strapped with 2×4″‘s – Roof is Fully Vented with a 3″ Airspace along ALL rafter bays.
6) 14″ I-joist Rafters
7) Amvic 1/2″ SiverBoard Foam Board – Glued, Taped and Foamed to INSIDE I-Joist Flange. R 2.1- this is bottom of the ventilation channel

My question:

I would like to fill the remainder of the cavity with Roxul Comfort Batt to R-44 and then
slip in a 1″ Dow Corning Foamular Pink Board R 3.0 on the inside of the bottom flange to create a Foam-Roxul-Foam Sandwich – Total R Value approx: R-46. This would of course be taped and foamed along all seams. Would this provide an adequate Foam/Soft Insulation Ratio or will I have to increase the amount of foam under the Amvic SilverBoard?

If this is OK? I would then proceed to seal the ceiling with 6mil poly using Acoustical Caulk and Builder’s Tape. Note: There will NO pot lights installed anywhere in the ceiling. We would finish off the ceiling with 1×6′ T&G Knotty Pine. My goal is to make this ceiling as airtight as possible. Spraying foam is out of the question as I’m in a rural area – the cost will be exorbitant and I would like to do the insulation myself to keep our costs down.

Thank you for your help and advice.

Mark Kozlowski
Vancouver, BC
Canada

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Mark,
    The product you are talking about -- Amvic 1/2" SilverBoard -- is foam-faced EPS. The foam facings are perforated, so the product has a permeance of 3.48 perms. So it isn't a total vapor barrier.

    Your plan to use XPS on the interior isn't particularly worrisome from a water vapor perspective. The worry is that you won't have a durable interior air barrier.

    The 1x6 pine boards are obviously not an air barrier. Over time, XPS rigid foam can shrink, so it's not a particularly robust air barrier. If you want to use interior rigid foam on your ceiling, you can -- but I would also install either taped drywall or a high-quality European air barrier material, carefully taped, to be sure that you have a good interior air barrier.

  2. charlie_sullivan | | #2

    Another option would be foil-faced polyiso, with taped seams. The foil provides a good surface for foil tape or other tape to grip.