In a phased approach to renovation, which should I do first: roof, siding and windows, or boiler?

BH2os | Posted in General Questions on

I have a home that was built in the 1980s in Northeast Kingdom of Vermont (Zone 6). It’s a 2-story cape with a shed dormer. It is a second home that sits closed up for a good part of the year right now but in 10years it could be a primary residence. A recent paint job failed which prompted me to investigate re siding. Then discovered the concept of adding insulation under the siding and all the complexities therein.

First off because of older construction practice of using poly under the drywall, what are my options for adding insulation on the outside of the sheathing? If I can add outside insulation then I think I have to re roof first to create “space” for the added thickness?

Thanks in advance.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Benedict,
    There is no single answer to your question. As I have often pointed out, you shouldn't replace your windows if you expect the investment to save you money. It would probably take you 50 or 80 years to save enough energy to pay for new windows.

    However, if you want new windows, get the best ones you can afford. I'm partial to triple-glazed Canadian windows with fiberglass frames.

    If your roof is leaking, you should obviously replace the roof first. If your roof isn't leaking, start with any job you want to see done. If you are planning new windows and new siding, those two elements of the job should happen at the same time.

    When your siding is being stripped, look at the sheathing carefully for signs of moisture intrusion, staining, or rot. If you sheathing is dry and sound, I wouldn't hesitate to install thick exterior foam, regardless of the 6-mil poly on the interior. Just be sure your contractor does a careful job of flashing windows, doors, and penetrations -- and include a rainscreen between the siding and the foam.

  2. BH2os | | #2

    Thanks Martin -

    A preliminary check behind the current siding (cedar) showed moist 30# felt. The OSB was OK at least in this spot. This area is on the South side that exhibited the most paint problems. My plan was to strip down to the sheathing, add Tyvek Drainwrap, then 1" (is that enough?) EPS, furring, then Hardie. What do you think?

    I'm assuming I can't use the foil-backed rigid correct?

  3. GBA Editor
    Martin Holladay | | #3

    Benedict,
    In Vermont (climate zone 6), your foam sheathing needs to have a minimum R-value of R-7.5 (if you have 2x4 walls) or R-11.25 (if you have 2x6 walls). This is the minimum R-value to maintain the sheathing above the dew point, which is important if you want to prevent condensation in your wall.

    I think you are wise to choose EPS rather than foil-faced polyiso, in light of the fact that your walls have interior poly. If you assume that the EPS has an R-value of 3.9 per inch, you need at least 2 inches of EPS over a 2x4 wall, or 3 inches of EPS over a 2x6 wall.

  4. BH2os | | #4

    Martin -
    Rainscreen = furring strips? Should those be treated or painted do you think?
    Are there schematics that I could give my contractor as the the best way to deal with the windows, doors etc..when adding the insulation to the outside?

    What seemed at the start to be simple looks trickier be the minute.

    Thanks for your help,

    Ben

  5. GBA Editor
    Martin Holladay | | #5

    Benedict,
    Yes, vertical furring strips can be used to create a rainscreen. You can also use a three-dimensional plastic mesh like Cedar Breather.

    If you (or your contractor) wants to learn more about flashing details for rainscreen siding applications, I suggest the following resources:

    The Stategies and Details page at GBA

    The EEBA Water Management Guide

    The Builder's Guide to Cold Climates from the Building Science Corporation.

  6. BH2os | | #6

    Martin -
    I DO need the WRB on the sheathing correct?

    So a good wall system could be:

    Drywall
    Poly
    2x 4 w/ Batts
    OSB
    DrainWrap
    2" ESP
    Home Slicker/Furring Strips
    Hardie

    Thanks again

  7. GBA Editor
    Martin Holladay | | #7

    Benedict,
    Your WRB can go between the sheathing and the foam or it can be installed on top of the foam. Some builders even put a WRB in both locations. But your decision to put the WRB over the sheathing is fine.

    I know that you are planning a retrofit of an existing house. But you asked about a "good" wall system, so I feel duty-bound to note that some of the existing features of your wall are not optimal.

    1. In a good wall system, you would omit the polyethylene.

    2. In a good wall system, you would fill the studs with some type of insulation that is more resistant to air flow than fiberglass batts.

    3. In a good wall system, plywood would be preferable to OSB.

    That said, your retrofit plan is a good one, and there isn't any need to change the poly, batts, or OSB.

  8. BH2os | | #8

    Thanks for your help Martin. It won't be perfect. But it will be better.

  9. BH2os | | #9

    I'm about to finalize my siding and exterior insulation plan and had a couple of questions.

    As I mentioned above I was going to use Tyvek Drainwrap as a WRB over the OSB and under 2" of EPS foam. Do you think the "channeled" nature of the Drainwrap would cause any significant airspace that would degrade the warmth of the wall cavity? Should I use plain Housewrap instead?

    And should I use one layer of 2" EPS or 2 layers of 1" or doesn't it matter?

    Thanks for any insight
    Ben

  10. GBA Editor
    Martin Holladay | | #10

    Ben,
    Q: "Do you think the 'channeled' nature of the Drainwrap would cause any significant airspace that would degrade the warmth of the wall cavity?"
    A: No. In this location, Drainwrap is a better choice than plain housewrap.

    Q: "Should I use one layer of 2" EPS or 2 layers of 1" EPS?"
    A. Two layers of 1-inch EPS (with seams staggered both horizontally and vertically) will perform better than one layer of 2-inch EPS, because there will be less air leakage and heat flow at the seams.

  11. BH2os | | #11

    Thanks for the clarification Martin.

    Should the seams be taped in this installation of the foam?

    And lastly, as to furring strips, does anyone have ideas as to the most appropriate material to use?

    Plane wood
    Primed wood
    Pressure treated
    Plywood
    Trex
    Metal

    Thanks again

  12. GBA Editor
    Martin Holladay | | #12

    Benedict,
    I would tape the top layer of foam. Ordinary unpainted softwood strapping should be fine.