Improving panned return ducts

runner9 | Posted in Energy Efficiency and Durability on

Our bungalow is a standard setup, with a 2 story addition added later. In the whole house, best I can tell, there are 3 return ducts, all on outside walls of the original house (1 is now interior), all on the 1st floor and all panned. I can access some of them from the basement.

The 2 farthest from the furnace are panned across to the center of the house, then in a duct going below the joists, then back into a panned duct that goes above the duct pushing air out, and then into another duct that goes back to the furnace, if that makes sense.

Is it better/more efficient/cost efficient to:

1. remove the drywall type product used to box in the floor joists where I can reach it, seal the inside of the other three sides as best I can, then attached new drywall or sheet metal to form a new bottom and also seal that, or

2. tear out the sections I can reach and install new metal ducts?

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Jeremy,
    Panned ducts are never a good idea, and are a code violation in most jurisdictions.

    You need to install new return-air ducts. Make sure that they are adequately sized; many return-air systems are undersized. Galvanized ducts are preferable to flex ducts.

    If the return-air system uses stud bays as ducts, you need to re-route the ducts. If these empty stud bays are on exterior walls, you need to fill the empty stud bays with insulation.

Log in or create an account to post an answer.