I’m not sure that my building inspector understands the science
![](https://secure.gravatar.com/avatar/6e1423bd4f1d9380f76baae81b020f85?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fi.png&r=g)
I live in climate zone 4A (near Philadelphia, PA) and I am building a 2400 sq ft addition on the back of my house. From the outside in, my wall assembly is vinyl siding, rainscreen, 2″ XPS rigid foam, zip-system sheathing, 2×6 stud framing with Roxul insulation. My building inspector says that I must have an interior vapor barrier. To the best of my knowledge (and research) with the exterior XPS on the wall, the interior of my wall should be vapor-open. I’m not sure that my building inspector understands the science behind leaving the interior vapor-open. Will a “smart” vapor retarder solve my dilemma? Is there an exception with the 2007 IRC that I can look to?
Thanks Ian
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
![](https://www.greenbuildingadvisor.com/app/themes/greenbuildingadvisor/dist/img/modules/detail-library/thumb1.png)
![](https://www.greenbuildingadvisor.com/app/themes/greenbuildingadvisor/dist/img/modules/detail-library/thumb2.png)
Replies
Ian,
Tell your inspector to look up Table N1102.5.1 in the 2007 Supplement to the IRC.
More info here: Calculating the Minimum Thickness of Rigid Foam Sheathing.
Ian,
Q. "Will a smart vapor retarder solve my dilemma?"
A. Yes. As building scientist John Straube has said -- I quoted him in my article, Smart Vapor Retarders for Walls and Roofs -- sometimes “the smart material really solved a building official problem, not a building science problem.”
Thanks for the information. 1 more question...My township follows the 2009 IRC, will the 2007 table you referenced still apply?
IRC 2009 has the same wall prescriptives for vapor retarders in SECTION R601:
http://publicecodes.cyberregs.com/icod/irc/2009/icod_irc_2009_6_sec001.htm