IBC Airtightness conversion
![](https://secure.gravatar.com/avatar/aff0370d23a0cd077ff933f84378f561?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fr.png&r=g)
eyremountllc
| Posted in Building Code Questions on
How do you convert cfm/sq. ft. @ 75 Pa to ACH 50?
Thanks!
Roger,
I don't know of any way to convert cfm per square foot @ 75 Pascals pressure difference to ach50.
Do you know cfm/sq.ft. @ 50 Pascals -- otherwise known as cfm50?
To calculate air changes per hour at 50 Pa (ACH @ 50 Pa or ach50), multiply cfm50 by 60 minutes per hour and divide the product by the building volume, including the basement, measured in cubic feet.
you can't...... if you don't know the envelope area of the building and the volume of the building.....
if you do, you can figure it out - although you would need to use an approximate conversion factor to account for the pressure difference. Infiltec list this as a 1.30 factor to convert the flow rate (cfm)
http://www.infiltec.com/inf-larg.htm
Keep it tight!
Thanks Martin and Floris! That's what I thought after doing some research too.
Thanks