I live in Iowa and I want to know if it is necessary to have a vapor burrier on my ceiling if I have roof vents
cwalker1965
| Posted in General Questions on
I’m also considering installing an attic exhaust fan, not sure how to determine the size of fan I need.
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Search and download construction details
Replies
In climate zones 5 & 6 you don't need a ceiling vapor barrier. The ceiling needs to be air tight however. Soffit to ridge venting is preferred, with the cross section of the soffit vent area 30-50% larger than the ridge vent area. Larger soffit than ridge vent area keeps the pressure difference between the conditioned & attic spaces at the ceiling plane limited, so as not to drive infiltration through the ceiling leaks with the stack effect of the attic height.
Attic exhaust fans are a universally BAD idea in reasonably insulated houses, especially in cold climates. Depressurizing the attic draws conditioned space air into the attic through any & all leaks in the ceiling plane, which increases the heating & cooling loads. In hot climates small self-powered attic ventilators can sometimes reduce total energy use in houses with sub-code insulation levels, provided there is sufficient cross section to the soffit or gable vents to limit the amount of depressurization.
Chris,
Dana Dorsett gave you good advice.
For more information on these issues, see:
Do I Need a Vapor Retarder?
All About Attic Venting
Fans in the Attic: Do They Help or Do They Hurt?