How to Design Mini Split System for Walkout Basement
![](https://secure.gravatar.com/avatar/24f105d302584d56c48e5784ccc50e3c?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fj.png&r=g)
I just came upon your website a few days ago while searching for answers to my question. The more I read, the more I’m finding that I’m not considering all the variables that affect the size, type and location of heads within a given space. Where to start? I have thought about reaching out to a local mechanical engineer to request services but seems that my 900 sf space would be no more than an afterthought.
>"Where to start?"
Start with a room by room load calculation (Manual-J or similar). If you don't have pro-software to use, try online freebies/cheapies such as Loadcalc.net or coolcalc.com, and be super aggressive on air tightness assumptions & R-values or they will oversize from reality by a large margin.
But in most places a code-minimum 900' basement would have both heating & cooling loads well under the output of a 3/4 ton minisplit, unless the walk out side is a long wall of glass sliders or something.
If there are multiple doored-off spaces with significant loads you'll probably need to go with a mini-duct cassette rather than a high wall coil type.