How do you reconcile continuous insulation requirements with rated assembly requirements?

user-1017842 | Posted in Building Code Questions on

The application is multifamily construction. We have energy requirements stipulating continuous R-3 insulation, in addition to required cavity insulation. We also have rated exterior wall assembly requirements.

I have not found any UL or GA assemblies that work, nor have I found any SIS product that has been UL tested.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
    Dana Dorsett | | #1

    Half inch fire-rated rigid polyiso, mayhaps? What UL test does it need to meet?

  2. user-1017842 | | #2

    U356 and/or U305

  3. Expert Member
  4. user-1017842 | | #4

    Thanks for the help!