How do published commercial and residential code requirements for combinations of continuous insulation and stud cavity insulation relate to in-wall condensation concerns?

user-198087 | Posted in Energy Efficiency and Durability on

The 2012 IECC includes minimum requirements for continuous insulation in combination with stud cavity insulation for wood stud walls. The requirements for these combinations differ between commercial and residential buildings. The required R values for continuous insulation are higher for residential buildings than for commercial. Considering cold climate applications, how do these requirements relate to in-wall condensation concerns?

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Albert,
    Q. "Considering cold climate applications, how do these requirements relate to in-wall condensation concerns?"

    A. They don't. Following minimum code requirements is no guarantee that you won't have a wet wall. These are minimum requirements, not optimal recommendations. To stay out of trouble, you sometimes have to exceed minimum code requirements for minimum foam thickness.

    For more information, see Calculating the Minimum Thickness of Rigid Foam Sheathing.