How do I thicken slab with 2″ of foam underneath?
![](https://secure.gravatar.com/avatar/8c5bfc5bf5694137fca2bc52b2316145?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fc.png&r=g)
I am building a house on a slab (with in-floor heat). There will be 2″ of blueboard underneath the entire slab. I need to thicken the concrete slab16″x8″x10 feet in the center. How do I do this and maintain the continuity of the insulation? Pour the pads first? Cut holes in the blueboard? Help, I start next week!
Charles,
You have three choices:
1. Increase the thickness of the entire slab so that the slab can support the bearing loads required. You should consult an engineer if you go this route. Most "raft slab" foundations do it this way.
2. Install extra insulation in the areas where the slab is thinner.
3. Rake the crushed stone to conform to the shape of the thicker concrete, and install 2 inches of foam on a slope where necessary. (Later edit: see Armando Cobo's comment: he advises using pins to hold the foam in place.)
What if I made boxes the shape of the thickened slab (with the top open). lay out the full sheets of blueboard and mark where the boxes belong, cut out the layer of blueboard and mark where the boxes should drop down, pull up the layer of blueboard and bury the boxes, lay the blueboard back down around the boxes. If you pour the thickened boxes first. it should work. Correct?
We always do the following detail with no problems ever... (you need to add appropriate rebar)
Armando,
I guess you choose option #3 -- I'm glad that it works (as long as you use pins).