Hot roof in Massachusetts?
mFK35Pqseu | Posted in Energy Efficiency and Durability on
I have 2×10 rafters with a new roof. Can I use Demilec AgriBalance open-cell spray foam?
They tell me it has an R-value of 4.5. My main concern is using 3/4″ tongue-and-groove pine for the ceiling. Should I use a vapor barrier or not? Thinking of using CertainTeed MemBrain. Do not want mold issues.
Thank you for any input.
  1. GBA Editor
    Martin Holladay | | #1
    Jim,
    Q. "Can I use Demilec AgriBalance open-cell spray foam?"
    A. Yes, as long as you use enough to achieve minimum code requirements. Since that product has an R-value of R-4.5 per inch, so you would need to install at least 8.5 inches of foam to achieve R-38.
    Q. "My main concern is using 3/4" tongue-and-groove pine for the ceiling. Should I use a vapor barrier or not? Thinking of using CertainTeed MemBrain."
    A. You don't need a vapor barrier. However, the building code in cold climates usually requires a vapor retarder. If you install 8.5 inches of spray foam, that qualifies as a vapor retarder and an air barrier. Be careful, though: if you switch to a different type of insulation, especially fiberglass batts, you definitely need an air barrier. Tongue-and-groove boards are not an air barrier.
  2. mFK35Pqseu | | #2
    do you have any input on the certainteed membrain. thanks for the info.
  3. GBA Editor
    Martin Holladay | | #3
    Jim,
    MemBrain is a vapor retarder; because it has a variable permeance, it is often called a "smart" vapor retarder. It is usually used on the interior side of walls or ceilings that are insulated with fiberglass batts, cellulose, or blown-in fiberglass.
    Since you plan to use spray-polyurethane foam, which is already a vapor retarder, you don't need MemBrain.
  4. mFK35Pqseu | | #4
    If the building inspector insists would this be the product of choice
  5. wjrobinson | | #5
    Jim, membrain should be fine, the makers of products are the ones to truly ask though. Get your sprayfoam company together with the inspector. Last point, a sprayfoam company worth hiring would have done many installs like yours and know how to handle the barrier/inspector/membrain issue for your particular home and climate. My last sprayfoam project had a vapor barrier paint sprayed on it to comply with inspector.