Hot-Climate Design Best Practices
![](https://secure.gravatar.com/avatar/300f2754c34c0edfefffee33f134f18a?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fd.png&r=g)
I’m designing a single story (+/- 3,000 SqFt) home in East central Florida (between zone 1a & 2a), less than a half mile from the beach – on a barrier island.
Is Martin’s article, Hot-Climate Design (10/9/2009) still representative of best practices (see below)? Additional thoughts regarding the foundation, wall insulation, air sealing, windows and roof would be appreciated.
Some considerations:
1. Concrete block is the doninant construction material and currently my most practical choice.
2. Slab foundations are typical (would a stem-wall be worth the investment?).
3. For decades, the “Space Coast” has been remarkably fortunate and has been spared severe hurricane impacts. That said, the EAST CENTRAL FLORIDA SURGE DEPTH ATLAS (link below) suggests a storm surge from a Category 3 hurricane might (just) exceed the 10′ elevation of my site. http://www.cfgis.org/HostedCFGIS/DigitalPlan/ECFRPC/DepthAtlas_Volusia_FrontMatter.pdf
Best Practices (from the article)
- Orient the house with the long axis east-west.
- A slab foundation should have perimeter insulation (unless termite concerns preclude it) but no sub-slab insulation. Uninsulated slabs can actually reduce a home’s cooling load.
- Shade is good. Roofs should have wide overhangs, ideally 3 feet wide or wider. Hurricanes like to grab onto roof overhangs, though, so be sure to secure roof trusses or rafters to top plates with adequate hurricane clips. Since a hipped roof can shade all four sides of a house, hipped roofs are preferable to gable roofs.
- Most windows should face north or south. Because they are harder to shade, east- and west-facing windows contribute much more to overheating than north- or south-facing windows; so east- and west-facing windows should be minimized.
- Every effort should be made to shade every window. Windows can be recessed into thick walls or protected by projecting architectural elements. On the east and west elevations, it’s often best to protect any windows with a wide porch.
- It is critical for a home’s air handler and all ductwork to be within the home’s thermal envelope. One way to do this is to “cathedralize” the attic by spraying closed-cell foam insulation against the underside of the roof sheathing. Of course, duct seams should always be carefully sealed; slightly oversized ducts are better than undersized ducts.
- Ceilings or roofs should be insulated to at least R-30.
- If the house has an unconditioned attic, specify radiant-barrier roof sheathing.
- Use highly reflective roofing — ideally, white metal roofing or white concrete tile roofing.
- Wall insulation is much less crucial down south than it is up north; 2 inches of rigid foam (R-10) is probably plenty. If the house has concrete-block walls, install the insulation on the exterior, not the interior.
- Specify windows with a solar heat-gain coefficient (SHGC) below 0.32; if possible, aim for 0.28 or 0.29.
- The home’s thermal envelope should be carefully air sealed.
- While high internal loads — that is, waste heat from lights and appliances — benefit cold-climate houses in winter, such loads hurt the performance of hot-climate houses in summer. So in Florida and Texas, it’s particularly important to install CFLs or LEDs rather than incandescent bulbs and to specify the most efficient available appliances, including refrigerators and televisions.
- Ceramic tile floors are best. Avoid carpeting.
https://www.greenbuildingadvisor.com/article/hot-climate-design
Musings of an Energy Nerd
Hot-Climate Design
Appropriate details help keep a house cool
1 addition: Solar PV prices per watt have dropped tremendously since 2009. Might change the cost benefit analysis for other energy saving tips.
I would add in there future water levels, both expected as well as max from larger storms.