Horizontal furring to break thermal bridging on wall studs?

MrDIY | Posted in Green Building Techniques on

I am about to hang drywall in my remodeled garage conversion. I’ve already had open cell foam sprayed to fill the 2×4 wall cavities. (I’m in TN, zone 4.) I’ve been reading about Mooney walls, and I’m sorry I learned all that AFTER the spray foam installation. My question is, would it be worthwhile to add a layer of horizontal furring before hanging the drywall, just to break the thermal bridging of the studs? I am considering using 1×2 furring to minimize cost, and it’s a (mostly) DIY so I’m not too concerned with labor.
Thanks, to any who reply and generally to this awesome forum for existing!

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
    Dana Dorsett | | #1

    A simple air gap created by the furring isn't much of a thermal break- about R1, reducing the heat transfer through the framing faction by about 20-23%.

    At the same wall thickness installing a continuous layer of 3/4" polyiso (R5-ish) would more than double the R-value of the framing fraction, reducing it's heat transfer by more than 50%, and reducing the heat flow at center cavity by about 25-30%. Long-nailing drywall to the studs through 3/4" polyiso isn't a problem. This solution would bring the wall performance fully up to IRC 2018 "R13 +5" code minimum for zone 4.

    If a full layer of 3/4" polyiso breaks the budget, cutting 4" wide strips of polyiso centered on the studs will thermally break the framing fraction, without boosting the performance at center cavity, at only 1/4 the amount of polyiso.

    1. Expert Member
      MALCOLM TAYLOR | | #2

      Dana,

      I was going to suggest foam strips as an alternative, but had no idea how wide they should be. The 4" rather than say 2" is because?

    2. MrDIY | | #6

      Thanks for your response! The mysteries off heat flow are slowly being revealed to me as I embark on this project - never to late to learn though. I'll cost out the polyiso and select one of the options you suggest.

  2. Expert Member
    Dana Dorsett | | #3

    At 2" if misaligned you may not get the full R-5 at the corner of the stud edge. A 3D THERM model would also easily show the improved benefit that comes from having that ~1.25" nominal overhang onto the open cell foam. The cold stud is making the open cell foam an inch away from the stud colder than it is mid-way between the studs. Another R5 over the cooler fringes of open cell foam is still "worth it" , with a much higher bang/buck than adding another R5 at center-cavity.

    The cold-fringing of the cavity fill near the studs is pretty obvious when looking closely with a thermal imaging camera, if you've ever had occasion to play with IR cameras. Those fringes aren't just 1.5" or 2" wide:

    https://encrypted-tbn0.gstatic.com/images?q=tbn:ANd9GcQ0Q0EEQ7zWOfwmnfmzy_7bNEmeWE9bU-vAmo_i8lOoQ0A8h4tJ

    1. Expert Member
      MALCOLM TAYLOR | | #4

      Thanks. That's exactly what I needed to know.

      1. Expert Member
        Dana Dorsett | | #5

        Malcolm: Here's a slice of a simple studwall modeled in 2D THERM:

        https://www.buildingconsulting.ca/images/22x6wallwoodinsulation.jpg

        The same model in pseudocolor (IR camera style) rather than isotherm lines:

        https://www.buildingconsulting.ca/images/22x6wallwoodinsulation3.jpg

        (clipped from this page: https://www.buildingconsulting.ca/therm-examples )

        The first inch or so either side of the stud is clearly takes the lion's share of the additional performance gain. Even 6" wide strips might be reasonable, but if you're going that far with it you might as well just do a full continuous layer.

  3. MrDIY | | #7

    Another problem I created for myself is on the ceiling / roof (the ceiling is being raised to the rafters except in the center of the space). I had a misunderstanding with the foam guy and he sprayed open cell to fill the 2 x 6 cavity. (I was expecting all closed cell but he only used it in the crawl space.) I am now planning to attach 2x4's perpendicular to the rafters and spray that cavity with closed cell. Any issues I should be aware of there - or better ideas?
    THANKS AGAIN!

  4. seabornman | | #8

    Keep in mind that adding foam to interior will require added wood nailers at corners and possibly ceiling and makes you think about electrical outlet installation.

  5. MrDIY | | #9

    Yes I've thought of that - a PITA but not a deal breaker. I'll likely add extensions. I could just yank them and re-install but then I'd have to re-foam those spots - so probably not worth it the extra effort