HEPA in an ERV – Beyond MERV 16?

alexdorf | Posted in Mechanicals on

While I’m sure we can get into the semantics of whether a building even needs this level of filtration – I’m just curious about the options out there, especially when clients start doing their own research and ask “what about HEPA?”

Are there any ERVS that will work with a HEPA filter? or a MERV 16? 

Follow up, do these filters present too much restriction in air flow?

Cheers,

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. DennisWood | | #1

    You can for sure use much higher levels of filtration for HRV/ERV. To reduce restriction you need to use external filter boxes, and look at 2" to 4" filters. This chart demonstrates the hit you'd take on your static pressure/flow using a 16x16x2 Merv 11 prefilter + 16x16x2 HEPA filter ducted at 6".

    https://www.hvacquick.com/products/residential/Indoor-Air-Quality/Inline-Filter-Boxes/HVACQuick-CFB-HP-Series-HEPA-Inline-Filter-Box

    You can achieve much lower pressure drops by using filter boxes that host larger (like 24x24x2) filters arranged in a 2-4 filter array.

  2. alexdorf | | #2

    Thank you for sharing, exactly the info I was looking for!

  3. DennisWood | | #3

    No worries :-) I just installed the 6" MERV 13 version of that box and measured minimal pressure drop (less than .1 W.C) across it at around 90 CFM using a 14x14x4 filter.