For a large scissor truss (top chord 31″ above bottom chord), we want around R-70 but no more
![](https://secure.gravatar.com/avatar/52b809068d1571e4f7f1bcb57b9091f8?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fd.png&r=g)
For a large scissor truss (top chord 31″ above bottom chord), we want around R-70 but no more. How do you ‘contain’ the blown in, or how would you use batts?
Here is the image
Damp sprayed cellulose blown in netting works. The damp sprayed goods have water activeated adhesives to keep it from sliding down the slope over time. If vented above it'll dry a a reasonable rate after installation even at R70 levels.
Dana, are you talking about netting above or below the insulation? I assume above, but it seems like it would be difficult to net that plane within the truss chords. As much as I hate batts, it seems like something that holds its shape is going to be a lot easier to do.
Yes, batts are easier to install, but will be guaranteed to have gaps. It's next to impossible to do a really GOOD job with R70 worth of batt in any open web truss.
If it can be installed from above you don't really need the netting, just depth gauges and a competent insulation crew, but that would be a pretty awkward installation in most scissor trusses.
The answer might be to have a carpenter install backing, then baffles of thin plywood or maybe rigid foam, then the wet cells. You could ask the truss company to factory-install something to make the baffling or netting easier, but they might look at you funny.