Foam over roof question
I asked this the other day but never got an answer.
When you are adding foam on top of the roof deck to create a sealed assembly do you typically go all the way out the the eave/overhangs or do you stop at the buildings thermal envelope (above exterior wall)?
Thanks
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
With deep overhangs it's common to only run the roof foam a handful of inches beyond the exterior of the wall's top plate (and any sheathing insulation.) With shallow overhangs it's less work to just run it out to the edge of the roof, even if it's over a soffit area.
Joe,
In almost all cases, you cover the entire roof -- because it's just as expensive to come up with a system of shims to cover the overhang as it is to use 100% rigid foam.
Hi Joe -
If you build a "flush" box and add overhangs AFTER you complete the roof frame and insulation, you have a better opportunity to completely connect the wall and roof air and thermal control layers (you ladder frame the overhangs and attach them as an "appendage"). In this case, you don't run the rigid insulation any further than the eave wall.
Peter