Is there a siding product that can be installed over 7/16″ sheathing with 2″ of rigid foam on the outside using advanced framing 24″ oc studs?

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
    Dana Dorsett | | #1

    Most siding can be installed over 2" foam on 24" o.c. AF stud framing, but most will require 1x furring through-screwed to the studs with timber screws, penetrating the studs by at 1.5" or more. Some vinyl siding products aren't design to be readily compatible with 24" o.c. fastener spacing, but most siding types can be mounted on 24" o.c. furring.

    There are purpose designed EIFS (faux-stucco on foam) siding solutions that would not need the furring.

    1. Coop54 | | #2

      Dana, sorry I forgot the furring strips. I wanted to use LP Smartside but. everything I have read requires 16"oc. I will contact Diamond Kote and see what they require.
      Thanks!

  2. GBA Editor
    Martin Holladay | | #3

    Coop,
    You may want to check out an old Q&A thread on this issue: "Fiber cement siding over furring strips."

    Here's a relevant section from my comment on that thread:

    Hardie instructions permit the installation of their [fiber-cement siding] products on framing that is spaced 24 inches on center. The company also provides instructions for installations over furring strips.

    Here are links to two relevant documents:

    HardiePlank Lap Siding installation instructions

    Applying James Hardie Siding over Continuous Insulation and Non-Nailable Substrates

  3. Coop54 | | #4

    Thanks Martin, not a big fan of fiber-cement siding.
    I did get a response from LP Smart side and they have changed their instructions recently to include AF stud framing with up to 4" of styrofoam!