Exterior rigid foam

peaceonearth | Posted in Energy Efficiency and Durability on

I’m soon residing my house and plan to incorporate 2″ of exterior rigid foam (EPS). Is it a no-no, or is it okay to adjust the typical order of things by having 1″ of EPS, then strapping over that, and then a second layer of 1″ EPS. This makes for a 3/4″ space that is not typical. But is it a problem?

Thanks for any input/advice.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Howard,
    In general, it isn't a good idea to include an air space sandwiched between two layers of insulation. The main reason is that air leaks at the perimeter of the air space are likely -- and you'll end up with convection currents or air flow that reduces the thermal performance of the entire insulation assembly.

    If you ignore my advice and include an air space, the perimeter of the air space has to be meticulously air sealed.

    It makes much more sense to install 2 inches of rigid foam, followed by exterior furring strips to create a rainscreen gap, and then your siding.

  2. Sean_in_Montreal | | #2

    Hey Howard, having a 3/4” air gap between your 2 layers of 1” eps would essentially render the first layer a drainage plain, and have no R-value, and there are cheaper ways to do that. What would be your reason for doing it your way?
    Also where are you located? 2” might not be enough depending on where you are.
    Sean

  3. peaceonearth | | #3

    Thanks gents. I'm in zone 6, so should need R 7.5. The EPS is rated 4.2 per inch, so should be a little more than minimum. The main reason for considering this way of of doing the foam (which I likely won't now do) is the easier fastening. Fasteners can be shortened going thru strapping and 1" of foam, and then fastening vinyl siding thru 1" of foam into the strapping.

  4. GBA Editor
    Martin Holladay | | #4

    Howard,
    If you really want the furring strips for the vinyl siding, and are restricted to 1 inch of rigid foam between the vinyl siding and the furring strips, the best way to proceed would be to fill in the air spaces between the furring strips with 3/4-inch-thick rigid foam, installed in an airtight manner. That's fussy work, but it would provide the best performance.

  5. peaceonearth | | #5

    Thanks Martin. I was aware of that as on option, but did want to avoid the expense and fuss that would entail. But I may rethink that.