Exterior Insulation Detail and Moisture Risk

bobbyarndt | Posted in Green Building Techniques on

Currently designing a 2×6 wall assembly for a home in Minnesota – Climate zone 7.

The owner wants to use R-9 zip-r sheathing with fiberglass or rockwool batts for the 2×6 cavity. The reasoning for using R-9 is to get the advantage of exterior insulation but still thin enough to not warrant buying specialty tools or change the building process too much.

Here is his desired assembly:
-LP smartside lap siding
-3/8 plywood battens
-R-9 zip-R
– 2×6 wall with R21 fiberglass or mineral wool
– Smart Membrain vapor retarder
– 1/2″ drywall

Although this assembly may be bullet-proof in other climate zones – I’m worried this could be a risky assembly in climate zone 7.

From my understanding – in climate zone 7 you would need R-15 exterior insulation to eliminate the risk of condensation in the 2×6 wall cavity.  Is this still a large concern using zip-r where your sheathing will be nowhere near the condensation point in the wall?  what if you were to use a hydrophobic cavity insulation such as rockwool?  Would this still be a worrisome assembly if the wall could dry to the inside?

What if we were to step up to the R-12 zip sheathing?

We love the idea and simplicity of zip-r but making it work in climate zone 7 is a challenge.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. jwolfe1 | | #1

    What is especially confusing is that the IECC only calls for R20 cavity + r5 exterior insulation. That is even less than r9. I’m curious to hear what other think of zip r9 in climate zone 7.

    1. bobbyarndt | | #2

      I agree the code is misleading. Martin Holladay addressed this in this great article.

      https://www.greenbuildingadvisor.com/article/the-2012-code-encourages-risky-wall-strategies

      Im less concerned about building code and more concerned about the performance and durability of the assembly. Mostly - will i get condensation in the wall cavity - and if I do - is it enough to be concerned about?

  2. Expert Member
    Akos | | #3

    The R15 is for a wall with painted drywall as the vapor retarder. By adding the smart membrane, you can use less exterior rigid. You can read more about it bellow:

    https://www.buildingscience.com/documents/building-science-insights-newsletters/bsi-026-they-all-laughed