ERV and HRV efficacy requirements under 2015 IECC code
In the IECC 2015 table R403.6.1 it lists In-line fan must have a efficacy of 2.8cfm/watt, is that the requirements we would use for whole house mechanical ventilation units such as ERV and HRV units.
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
I don't believe that requirement applies to H/ERVs. If it does we're in trouble; only 20 of 375 HVI listed H/ERVs would meet it.
I agree, but is there a efficacy requirement for ERV/HRV unit or do you just enter the HVI rated power consumption or measure the actual power consumption and enter that in the HERS rating?