Enabling sheathing to dry on a low-slope unvented cathedral ceiling

Nilsk | Posted in Energy Efficiency and Durability on
I’m working on a project where I have an unvented low-slope cathedral ceiling and am worried I’m walking right into the rotten OSB SIPs trap. The building is in climate zone 6. The roof pitch is 2-12 and there is currently triflex installed on top of taped osb sheathing. On top of the installed sheathing there will be 5 inches of rigid foam, followed by an additional layer of osb sheathing wrapped in a peal and stick membrane followed by a standing seam metal roof.
This layup seems risky as the outermost layer of sheathing is trapped between impermeable layers. Most of the advice I have dug up recommends adding ventilation channels between metal roofing and sheathing. The problem I see with this is that with a 2-12 roof I feel I need to use something like Ice and Water on the whole roof, thus preventing drying towards the metal roofing. Is there a way to add ventilation channels underneath the top layer of sheathing? I was wondering if I could use strapping between the foam and sheathing layers to create ventilation channels. It seems like this would create some choice critter habitat along with a tricky fascia/drip edge detail. Is there a simpler way to do this? Should I just skip the ventilation and double down on air sealing in the ceiling/lower sheathing?
Many thanks for the help and invaluable resource.
Cheers,
Nils

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Nilsk | | #1

    Think I may have come up with a solution - ventilation channel tied into some sort of soffit vent a la cor-a-vent ps-400. Not sure why I was struggling with that so much.

  2. GBA Editor
    Martin Holladay | | #2

    Nils,
    Lots of unvented roofs include a layer of sheathing that is unable to dry in either direction. As long as the roof is otherwise well-detailed, this type of roof works fine.

    The key point: The weather has to be dry -- ideally, dry and sunny -- on the day that the sheathing is installed. You don't want to cover the sheathing will peel-and-stick if the sheathing is damp. As long as the sheathing is dry when it is encapsulated, you can sleep well at night and stop worrying.

Log in or create an account to post an answer.