Electric micro-boiler & temperature sensor
When it comes to modulating electric micro boilers like Seisco for radiant floor heat in a cold climate (zone 6a) with a well insulated garage and workshop space (R22 sub-slab, R46 above grade walls, R66 roof), is it better to choose a unit that just meets estimated Btu needs or go with a unit that will provide more Btu’s than estimated? (The units I’m considering the Seisco 09 or 11, both cost the same, so there isn’t a direct financial drawback to going with a larger unit outside of a larger gauge wire and larger amp circuit breaker.) The units self modulate so most of the time the kW use should be much lower than maximum rating.
Is there a drawback to going with the larger unit?
I’m also trying to see what folks think about thermostats – air vs. sensor (in slab). My initial thought is to go with the sensor (in-slab type) so that every time the garage door opens and cold air blows in, it doesn’t make the micro boiler cycle (as I assume it would with an air based thermostat). I’m assuming once the radiant slab is up to temp, it will buffer those instances where the garage door is open for a bit.
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
The drawback is higher peak draw, but unless your utility bill has demand charges for the peak draws (rare, for residential rate structures) and only bills out on an energy use basis it's no different.
A floor sensor is the right approach.