Hi,
I am wondering if this is an incorrect setup for our drain line and its connection to the vent? I have seen multiple posts online that a wye should not be used in this application, but it should be a sanitary tee. For the plumbers in here, can I get confirmation of this? My contractor, who is not using a licensed plumber but operating under the license of one, is adamant this is sufficient. My understanding is the way it’s setup now with the wye could allow for a strong enough siphon to pull water from the trap and allow sewer gas out the “wrong end.” It also appears to almost make an s-trap, but I think that’s debatable.
Thanks,
Michael
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
Not allowed and likely clearly evident in whatever code you're under. You are correct in saying it should be a sanitee.
Thank you for the confirmation! Glad to know I'm not crazy. Everyone should bear witness to the totality of this plumbing job and let it serve as a guide on exactly how not to plumb a house. It's so sloppy and bad.
Yep, should be a sanitary tee. There is a thread on almost exactly this setup on the Terry Love plumbing site: https://terrylove.com/forums/index.php?threads/best-way-to-wet-vent-a-washing-maching-and-utility-sink.83470/
JLC's field guide for venting may also be helpful here:
https://www.jlconline.com/how-to/plumbing/vents/vents-field-guide
I think you're pretty close to having an S trap here too, but if they replace that wye with a sanitary tee raised up a bit, then they'll probably have enough of a horizontal pipe section to get you back into P trap territory. Basically replace that one fitting, and swap the position a bit using a coupler, and you can fix both issues at once.
Bill
Thank you Bill for the reply and links. They will serve very helpful in my conversation. I also found a plumbing company that will come do a full inspection, so at least will get some peace of mind before everything is covered up and it's too late.
Not a plumber. But the reason a sanitary tee is required there is there has to be a continuous layer of air between the top of the pipe and the vent, otherwise the pipe can get airlocked under heavy flow.
Fixing it is less than $20 worth of fittings and a few minutes.
Thanks DC, that's my instinct too but all I get is pushback when I ask, cause I'm just a lowly homeowner. It's a pattern of behavior from our contractor and we're just safeguarding ourselves from future issues and trying to get to a point where we can let him go.
Thanks