Due to aesthetics, R-20 (4 1/2 inches of rigid foam) above the roof is my limit

designc | Posted in Green Building Techniques on

Due to aesthetics, R-20 (4 1/2 inches of rigid foam) above the roof is my limit. Would Roxul plus an airspace in the rafter bays be a good choice for the remainder of the needed R-value?

Jesse, 80% of home is concrete slab with remaining 20% being crawl space I closed in – conditioned basement. In a high water table area with no vapor barrier under slab or crawl. De-humidifier runs constantly.

I plan to include air space in rafter bays under sheathing along with batt insulation for remainder of needed R-value. Is an airspace necessary with R-20 foam above roof sheathing?

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Cameron,
    It looks like you intended to post this on a different page. In most cases, it makes sense to maintain just one thread for a series of questions, rather than starting a new thread each time.

    Here is a link to the original thread:
    https://www.greenbuildingadvisor.com/community/forum/green-building-techniques/36210/what-recommended-method-insulating-cathedral-ceiling

    It would be a good idea to post all answers back on that page.