Double-stud wall construction filled with Roxul

davidmateroarchitecture | Posted in Green Building Techniques on

I am in discussions with a contractor on how to insulate a staggered double-stud wall, 2×6 on the outside and 2×4 on the inside.

We can save a fair amount of money by filling each stud bay with Roxul and a layer of poly between the studs. I see this detail all the time with blown-in cellulose. What is the downside to 2 layers of Roxul in a staggered stud wall assembly?

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    David,
    Dense-packed cellulose will do a better job of reducing air leakage than Roxul. But Roxul should perform well if the installers do a careful job. Whichever insulation material you use, pay close attention to air sealing details.

    I don't know where you are located, but unless you are in a very cold climate, polyethylene shouldn't be included in your wall assembly.

  2. davidmateroarchitecture | | #2

    Martin, thank you. I forgot to mention I am zone 6, Brunswick, Maine. Poly between the studs was recommended by an insulator. In lieu of that do you suggest we tape/seal the sheathing? I was worried about the potential movement of stick built framing and Roxul, but the staggered studs will help with that. The install savings is rather significant over blown in that will help us in other places.

  3. user-1140531 | | #3

    Martin,

    According to my understanding, for permeable insulation, the air sealing would be essential at the interior surface of the wall. Regarding the avoidance of using poly except for very cold cliamtes: Aside from the consideration of climate zones to define this advice, what is the outdoor temperature which differentiates whether to use poly or not use it?

    Maybe this cannot be quantified because the decsion must factor how much time at the lowest temperature versus how much time at a higher temperature where drying can occur.

    But, in any case, I would like to know exactly the conditions where poly cannot be used versus where it can be used.

  4. GBA Editor
    Martin Holladay | | #4

    Ron,
    The best way to answer the question is with WUFI.

    One big variable: your indoor RH.

    Another big variable: your air leakage rate. The higher the air leakage rate, the riskier it is to use poly.

    A third big variable: the details of your wall assembly. Obviously, if you have exterior rigid foam, you don't want interior poly.

    A fourth big variable: whether or not the building will be air conditioned. Cooling the space in summer makes the use of poly more risky.

    In general, if the wall has no exterior foam, and if the building is air conditioned, I usually advise builders to avoid the use of interior poly unless they are in the colder parts of climate zone 6 (or anywhere colder, including most of Canada). Even in those regions, it's usually possible to design a wall assembly that doesn't need poly.