Hi,

I am at the stage where I need to finalize my decision for my roof, wall and slab assembly. Please let me know if I have missed something or if you have any comments and suggestions.

Sorry the assembly aren’t very professional looking but it’s the best I could do given the software (MS Paint) I have access to.

Thank you,
Arnold

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. arnoldk | | #1

    The attached assembly which did not attached with the original post.

    Arnold

  2. Expert Member
    Michael Maines | | #2

    Arnold, your assemblies look reasonable to me at first glance. What climate zone are you in?

    1. arnoldk | | #3

      Hi Michael,

      I am pretty confident in the wall assembly but I just want other pair of eyes to have a look at it just in case I have over looked it. I'm in Zone 6 (Ottawa, Canada).

      Thanks,
      Arnold

  3. Expert Member
    MALCOLM TAYLOR | | #4

    Arnold,

    They look good. A few small points.

    - You may want to extend the termite shield over to the slab to completely block potential access.
    - I'm not sure the exterior foam adds much for all the extra complication and expense. The wall will dry to the exterior much better without it.
    - Why a separate air and vapour barrier under the trusses?
    -The areas to clarify are how the wall intersects with what looks like a sec0nd floor (continuity of structural sheathing, air-sealing, etc), and the same at the roof.

    1. arnoldk | | #5

      Hi Malcolm,

      Thank you for the feedback and I will try to clarify those on the drawing especially the intersection of the floor joist of the second floor.

      The exterior rigid insulation (ComfortBoard) was to help hold the batt insulation in the 2x6 cavity wall and to added more thermal break, especially at the floor joist and the sill plate where it will overhang by 6 inches.
      I agree with you there will be additional work and cost with this approach and I need to figure out a way to cover the bottom where the ComfortBoard and rainscreen will overhang the slab by about 4 inches.

      I included a vapor barrier because I am assuming the Ottawa building inspector is going to want to see one despite the fiberboard air barrier. If it's not needed and the inspector does not require it, I will leave it out and save the cost of the material and my labor.

      Thank you again,
      Arnold

      1. Expert Member
        MALCOLM TAYLOR | | #6

        Arnold,

        I should stress again they are minor things things I've brought up, and the walls and roof will work very well the way you have drawn them.

        You may find this blog by a past frequent poster here on GBA useful for how to detail walls with no exterior sheathing. http://ourhouseuponmoosehill.blogspot.com/p/details.html