Does air sealing impact wind load capacity

millionsofpeaches | Posted in General Questions on

I’m picturing the homes with breakaway elements/panels and other similar details as those that survive storm surge during hurricane events… does making a home air tight (let’s say < 1 ACH50) make a house (windows?) more susceptible to high winds (60, 70, 80+ mph?) Or do wind load ratings perhaps already take ‘perfect installation’ into account?

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
    Michael Maines | | #1

    The only thing I'm aware of along those lines is that you can get impact-rated glazing for areas that are likely to experience wind-blown debris that could break the glass and allow in a gust powerful enough to blow the roof off. Alternatively, in those areas you can beef up the structure.

    When you're going from something like 3 or 7 ACH50 to 1 or less, the difference is a few square inches to a few dozen square inches of air leaks, usually spread all over the house, so I don't think airtightness would make a measurable difference for storm resistance.

  2. Expert Member
    BILL WICHERS | | #2

    In short, no, doing a good job of air sealing does not change the wind survival rating of a home. The amount of wind that leaks through little cracks and pinholes is so small as to be inconsequential in terms of force exerted (or, in this case, not exerted) on the structure. To visualize this, take eight sheets of plywood put together in a line to form a wall 32 feet long. Assume the builder is an avid reader of GBA, and taped all the seams between those panels so that the wall is perfectly airtight -- 0.0ACH50! Yeah!
    That's 256 square feet of surface area. With 50 mile per hour winds blowing straight into that wall, the wind is exerting about 1,638 pounds of force against the wall.

    Now let's assume you didn't tape the seams between sheets of plywood, and left 1/8" gaps between the sheets. Even worse, you didn't land the edges of the panels on studs (horrors!), so the wind can blow right through those gaps. There will be a total of seven of those gaps between the 8 sheets, and they'll total about 0.6 square feet of total area. That leaves 255.4 square feet of plywood surface for that same 50 MPH wind to blow against, but now only about 1,634 pounds is exerted on the wall.

    All those totally open seams only saved 4 pounds of wind force, which was about a 0.24% reduction in this example -- not enough to worry about. In an actual structure, there will probably be something behind the plywood (drywall, etc.), so the wind will still "hit" something and exert force, even if it ends up leaking through the wall eventually. Even with completely open seams, there are still some aerodynamic forces that are going to act on the airflow so that the "leaking air" still exerts a little force and doesn't quite completely sneak through that wall.

    I would say from an engineering perspective that wind forces on a structure assume a "perfect" air seal, since the calculation is just force over the area of a wall -- no allowance is made for holes in that wall. If your window blows out or the roof flies off, then that's a different story :-)

    Bill

  3. millionsofpeaches | | #3

    Awesome! Thank you both!