Does 1×3 strapping reduce thermal bridging?

dirkgently | Posted in GBA Pro Help on

For those not familiar with the term strapping it is 1×3 boards.
It seems to be a New England thing to install 1×3 perpendicular to ceiling joists prior to installing drywall on the ceiling.
Does this practice significantly reduce thermal bridging of Rafter/ceiling joists in a cathedral ceiling application?

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Farnum | | #1

    No, this is done strictly for the dry-waller's benefit. With batt insulation, strapping between the framing and the drywalling can actually create thermal bypasses if the paper is not face stapled, or increase convective looping if the other side is exposed to the air.

  2. Expert Member
    Dana Dorsett | | #2

    It actually does provide a modest thermal break, but it's nothing to write home about. The thermal performance of the horizontal air films in the 3/4" deep trapped space is about R0.6-0.9.

    That increases to about R2 with a foil facer on the top side of that cavity (still nothing to write home about.)

  3. charlie_sullivan | | #3

    But if you are blowing in cellulose, wouldn't it have more benefit than with batts?

  4. morganparis | | #4

    Your ceiling insulation should normally be twice the depth or more of the ceiling joists so the joists will be completely covered in 8" or so of insulation. There's your thermal break right there. I think we all wish walls were that easy.