Do you have to mechanically ventilate an attic space used for storage?

good4utoo | Posted in Building Code Questions on

Do you have to mechanically ventilate an attic space used for storage when the whole attic is within the thermal envelope? The roof is 10 inch SIP panels (R-60) and all walls are open-cell SPF.

The owners have asked if there is a code issue here. We can’t find anything definitive.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Ann,
    No, you don't want to ventilate a conditioned attic. Of course, if the house is very tight, you will want to install a mechanical ventilation system for the occupied areas of the home (living room, bedrooms, bathrooms, etc.). This can be done with an exhaust-only system, a supply-only system, or a balanced (HRV or ERV) system.

    If the attic is used for storage, it needs neither fresh supply air nor exhaust air.

    The section of the 2009 IRC that provides requirements for unvented conditioned attics is Section R806.4. For more information on this topic, see Creating a Conditioned Attic.