Crawlspace rim joist
![](https://secure.gravatar.com/avatar/3bbaea808a7fc032a4abf2d05ce31a66?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fc.png&r=g)
Hey All,
Have a crawlspace in zone 4A zip 08731. Installed a mini split a few years ago and it’s doinf a fine job heating the house until the crawlspace becomes cold due to no insulation down there. I eventually plan to do 2” of polyiso on the outside of the house but until the funds are ready to do that and the windows I am looking for a temporary hold over. Can I do 2.5” of EPS on interior of rim joist with foam sealing the edges and can it stay in place when the eventual exterior polyiso is installed?
Thanks!
Also thinking of throwing some spare Roxul into the cavity after the EPS. And where the ground meets the cement outside I would switch to XPS I got from a construction site from polyiso due to moisture issues with poly.
Yes, it's fine to install 2.5" EPS on the band joist & foundation sill. It's better to use un-faced EPS if you're planning to use foil faced foam on the exterior later. At 2.5" Type-II (1.5lbs per cubic foot nominal density) EPS runs about 1 perm, the boundary between Class-II and Class-III vapor redardency. In zone 4A you could also just caulk the seams and install carefully trimmed R15 rock wool batts. It's also possible to use 2" fiber-faced reclaimed roofing polyiso, which is usually cheaper than high density batts or virgin-stock EPS:
https://cnj.craigslist.org/search/sss?query=rigid+insulation
In zone 4C (the coastal Pacific Northwest ) you'd still want at least 3/4"-1" of EPS between the batts and band joist for dew point control, but in 4A it's not really necessary. At 1" Type-II EPS is between 2.5-3 perms, which is quite a bit more drying capacity, almost as vapor open as interior latex paint. See:
https://up.codes/viewer/utah/irc-2015/chapter/7/wall-covering#R702.7.1
On the foundation walls themselves stick with just the foam, no fiber. The foundation is usually 2-3x as thermally conductive than a band joist, so it's at least as important to insulate the above-grade portion foundation walls as it is to insulate the band joists. If using polyiso, don't let the cut bottom edge of the foam contact the soil, since polyiso is somewhat hygroscopic and will wick up moisture.
Thanks Dana for the detailed answer.
Chris,
Here are links to two articles that explain what you need to do:
Insulating rim joists
Building an Unvented Crawl Space
Hey guys was wondering about swapping the interior EPS for open cell foam in the joist bays. Would cost more but would save a lot of time. Would that still be vapor open enough if I were to add polyiso on the exterior of the rim eventually? Everything I’ve read including the links suggests closed cell but then no exterior foam.
Chris,
First of all, it sounds as if you are worried that the installation of closed-cell spray foam on the interior of your rim joist will preclude the installation of exterior polyiso. Your worries are unfounded. As long as your foundation wall includes some type of sill-seal between the top of the foundation wall and the mudsill, there is no need to worry about foam on both sides of the rim joist.
Second: The reason that most experts advise builders to use closed-cell spray foam rather than open-cell spray foam at the rim joist is that it is advantageous to stop outward vapor drive. You don't want moisture from the warm, humid interior to diffuse through the insulation layer and reach the cold rim joist. So closed-cell spray foam on the interior is better than open-cell spray foam.
The sooner you can get your exterior polyiso installed, the better (and the less this issue matters). Once the exterior polyiso is installed, the rim joist will be warm, and the open-cell spray foam would become safe. Before the exterior polyiso is installed, however, the use of open-cell spray foam is somewhat risky.
Adding it all up is complicated. The final decision depends in part on whether the installation of exterior polyiso is a certainty, or just a hoped-for dream.