Combustibles clearance BEHIND a fireplace
Hope this question isn’t too far afield of the GBA mission. I have lots of respect for people who comment here so hoping someone has run into this question before.
I’m looking for code, or physics illustrations, about heat dynamics above and behind a fireplace.
Situation: the front of a combustible (in this case a TV) is set back X inches from the back of a “zero-clearance” fireplace (in this case a direct vent, no fan). A mantel (quartz or steel) with min. 1” air gap could be placed above the fireplace unit if truly impactful.
The manual only speaks to and shows clearances directly above the unit, and in front of the unit. They do not speak to the area behind the unit except the 3” clearance from vent pipe (a non-issue in this case).
My hypothesis is that the area both behind and above the fireplace is zero-clearance. Otherwise the wall the fireplace is mounted on would require specifications to be non-combustible for at least 15” above the unit, which does not appear to be required at all.
Taken literally this would mean that combustibles set back just 1 mm behind the back of a zero-clearance fireplace could be 0mm from the top (but still 1mm from the back) of the unit. But common sense tells me that radiant heat doesn’t arbitrarily stop behind the fireplace. So it seems there may be (should be?) a guideline something like:
TYPICALLY, unless otherwise noted by the manufacturer, for every inch that combustibles are set behind the back of a zero-clearance fireplace the required vertical clearance is reduced by X%. (In reality would likely be non-linear drop-off rate, but you get the idea.) A diagram of typical heat range that includes the air behind the fireplace would be ideal.
I’ve been trying for hours over days to find clear guidance on areas behind/above fireplaces and can only find anecdotes and generalized advice unsupported by code or science or numbers.
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
Dave,
All the zero clearance fireplaces that I've installed that had small clearances to the box on the top, back or sides came with V shaped guards to offset the unit. In the absence of clear limits in the instruction manual, you can take them at their word it is a zero clearance fireplace.
To assuage any lingering fears, why not call a dealer that sells the unit you are considering?
Thanks, Malcom. This unit has no stand-offs since it hangs on the wall like a picture. Only 9" thick! I did speak to the dealer who gave me a green light as well. I also checked with National Fireplace Institute, no specific guidance to be had other than "better to be safe than sorry" but that doesn't help too much. If TV-damaging heat were my only concern there are $20-40 USB-powered fans you can mount on back of the TV that would likely mitigate that. What I am mainly concerned with is building inspection. So far it appears code requires I follow the manufacturer's instructions, which in this case doesn't include any prohibition about putting something combustible above AND behind the unit.
That's what our code says. It gives clearances, but only for site-build masonry fireplaces. For all others the manufacturer's instructions govern.