choosing drain plain material or no drain plain at all
option 1) 1/8″ waterway mesh vented at bottom (will I loose too much R value due to excessive air movement from chimney effect through any air leaks higher up the wall, no guarentee they will all be sealed)
I appreciate any help I can get, I have been stewing over this for way too long, but have been unable to get a definitive answer anywhere on GBA/ FHB / JLC
I am posting this on all three sites
Thanks Mike
PS pix shows bottom of wall and roofnado air block for waterway drainage path
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
Yes I have read "wrinkled-housewrap-behind-exterior-rigid-foam"
Michael,
Venting just the bottom is fine, although adding a top vent will not degrade the R-value of your walls.
Rain-screen gaps improve any wall, and if you ar going to add one it's worth making it effective - meaning at least a mesh uunderlayment, rather than bumpy house-wrap.
However, as you have an impermeable WRB you aren't going to get the benefit of drying to the outside a gap affords, just the benefit of the cladding drying better, so whether that's worth it in your climate I'm not sure.
Malcolm
thanks for your reply, this is concerning the drainage plain between the foam and the vapor closed P+S. ( Its sole purpose is to allow any water that ever gets behind the foam to have a way to escape ) I have a conventional 3/4 gap rain-screen between the outside of the foam and the hardie siding.
My concern is If I vent the top, would enough air move up the 1/8" gap to have a significant effect on the R value of the wall remember this is the drain plain not the rain screen
Michael,
Ah got it. I don't think a gap is necessary between the foam and WRB, but lets's see what others say.