CFM NEEDED FOR HOT TUB ROOM?

user-1072251 | Posted in Energy Efficiency and Durability on

Client wants to move Hot Tub indoors into it’s own 9×9 room. Whole house HRV will be running continuously; I will add dedicated exhaust fan; considering Panasonic Whisper, but have no idea how much ventilation will be needed to exhaust moisture when tub cover is off. Suggestions?

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. STEPHEN SHEEHY | | #1

    I've had a hot tub for many years in an unheated room. I originally installed an exhaust fan, but have never needed it. Assuming cover is off only when in use, at most run a small (100 cfm or so) when in use. I'd seriously recommend not heating the room.