user-6445625 | Posted in General Questions on

Hey folks,
For a house in Zone 6 we are looking to mount cedar shingles onto horizontal 2x battens directly on top of Comfortboard 80 exterior insulation. Normally we would double the rainscreen here by adding vertical elements behind the horizontal but I’ve been reading that it may not be necessary given the porosity of Comfortboard. Any thoughts on whether this will be an adequate rainscreen assembly?
thanks!
Brad

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Malcolm_Taylor | | #1

    brad17,

    From a practical perspective y0ur proposed assembly has almost all the attributes of a well functioning rain-screen, and I think will work fine.

    If you are in BC it won't meet code because it lacks a dedicated vertical drainage plane.

  2. user-6445625 | | #2

    Thank you!

    1. Malcolm_Taylor | | #3

      brad17,

      Thinking about it again...

      That's an awful lot of 2"x horizontal battens. You might still consider whether 1"x3"s both vertically and horizontally don't make more sense. It uses a lot less wood, and a lot less long fasteners.

  3. user-6445625 | | #4

    Good point thanks

  4. Expert Member
    KOHTA UENO | | #5

    A nice set of photos of a vertical batten-horizontal cross batten assembly with exterior shingles is on the 475 blog: https://foursevenfive.com/blog/from-post-office-to-postcarbon-future-with-emerald-builders/