Cathedral ceiling insulation
I recently read your cathedral ceiling insulation article. Attached is my preferred detail to allow for definite roof ventilation and 2 air barriers. There will be soffit vents at high and low points of roof. I need the rigid foam to prevent wind washing. Is the Membrain a problem?
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
Hi John -
To answer this question, need to know what climate zone you are in. For a vented roof assembly in Climate Zone 6, 7, or 8, a Class I or II vapor retarder on the "warm-in-winter" side of the assembly is required (and either of the two smart vapor retarders you cite complies).
Peter
Lexington, Virginia climate zone 4a
John,
In your climate zone, an interior vapor retarder is not required, so you can skip the MemBrain. However, if the MemBrain is already installed, it won't cause problems.
Remember that the drywall needs to be installed in an airtight manner (which means attention to airtightness at all penetrations).
The path to drying around 1" foam AND the flange of of the I-joist is pretty long. I'm not comfortable counting on that unless the foam is also fairly vapor permeable, such as unfaced Type-II EPS.
In zone 4A a minimum of 30% of the total R has to be on the exterior of the fiber insulation to have adequate dew point control at the foam/fiber boundary.
Rather than being a problem, the Membrain will mitigate the risk, but it isn't going to be sufficient to eliminate that risk.
Instead of 1" foam, 3" of foil faced polyiso (R19-ish) with 10" of low density fiberglass (not dense-packed blown or "cathedral ceiling" batt, for R37-ish performance @ 10") AND the Membrain would have a tiny bit of margin.
That makes sense. I will eliminate the 1”foam. I think this detail will work well and provide R52.