Cathedral Ceiling Insulation

ilovebatz1 | Posted in Expert Exchange Q&A on

I have a home built in 1978 that uses 2×12 rafters. There are fiberglass batts between the rafters, it looks like two 6″ paper faced bats with one paper face toward the roof deck and one toward the ceiling. 2/3 of the ceiling is smooth cedar planks. I need a new roof and need to know how to proceed. I was thinking of putting EPS panels on top of the existing sheathing to accomplish R-20. However based on the table about installing rigid foam above the sheathing, I will need 41% to be from the rigid foam. Using a figure of 3.7 R/inch of fiberglass bats, the thickness of the rigid foam would have to be R28. Does this make sense? Do I have to install this much rigid foam? One problem I will have is that I have clerestory windows which will not be able to tolerate even a 4″ added thickness of rigid foam. Any suggestions about this? Thank you very much for your advice.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Malcolm_Taylor | | #1

    ilovebatz1,

    The ratio is dependent on where you are. What climate zone are you in?

    1. ilovebatz1 | | #2

      I am climate zone 5, in eastern WA.

  2. Malcolm_Taylor | | #3

    ilovebatz1,

    Sorry - you are right. The existing batt insulation (roughly r-40) dictates the necessary (r-28) depth of the foam above. To me the complications of working from either the inside or exterior of the roof to get more R-value outweigh any gains you might see. I would look for low hanging fruit elsewhere, like air-sealing or other areas where the insulation is obviously too low.

    1. ilovebatz1 | | #4

      Malcolm, thank you for your replies. One of my concerns is about condensation on the underside of the deck if I leave everything as is. So far it doesn't seem that I have had a condensation problem but I have been using a whole house humidifer the last three years, set at 40% RH in the fall/winter/spring heating seasons. Is this likely to cause problems? My cathedral celing is unvented. Thank you.

      1. Malcolm_Taylor | | #5

        ilovebatz1,

        You are most likely to see moisture problems near the peak. Given the age of the house, if they haven't occurred yet, they probably won't.

        There are a number of effective assemblies you can retrofit, but all are very disruptive to either the exterior or inside - and your roof has a number of end and side-walls which if you add any height to the roof surface, will need the cladding removed for re-flashing. So the question becomes: in the absence of moisture issues, are they worth doing?

        1. ilovebatz1 | | #6

          Thanks again, Malcolm.

  3. FrankD | | #7

    I tend to agree with the "don't lose sleep over what isn't broken" philosophy, but I think you should have a plan in mind in case the roof tear-off does reveal rotted sheathing. When you say there doesn't seem to be a condensation problem, do you mean you removed some of the planks to have a look in there?

    Although most people just use the ratios implied by table R806.5, there is also the alternative in sentence 5.1.4 of calculating a ratio based on your average winter temperature. If you are in a relatively warm-in-winter part of CZ5, the required ratio might be closer to 35%.

    You might be overestimating the R-value of the batts. If they were installed when the house was built, they would most likely be R-19. Compressed into a 2x6 space, Owens Corning says the R-value drops to R-17 (https://dcpd6wotaa0mb.cloudfront.net/mdms/dms/Residential%20Insulation/10017857/10017857-Building-Insul-Compressed-R-Value-Chart-Tech-Bulletin.pdf).

    So hypothetically, if the batts are R-34 and the required ratio is 35%, you would only need R-18.5 on the exterior, doable with 3.5" of polyiso.

    1. ilovebatz1 | | #8

      Thank you Frank. This gives me some more things to think about. I haven't torn off any planks, although I am going to pull out the one can light that is in my living room ceiling. I do have a very small attic space and have looked at the insulation there. I have attached a picture of the roof deck that I could see along one of the rafter bays after moving some insulation.