Can I pass a sink drain pipe through a 12×12 wooden support beam in the basement?
Hello,
I want to install a sink on one side of the support beam (on the floor above) and the main drain is on the other side of the support beam (in the basement). I can’t pass it above the beam because it is the middle of the hallway. If I pass it under, it will be so low that we will have to bend to pass under the drain pipe. Is it acceptable to drill a 1 1/2″ hole through a 12″ x 12″ support beam. I have seen that the diameter of a hole should be maximum 1/4 the height of a joist, but does that apply to a support beam?
Please advise.
Thanks
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
L0ngfield,
The IRC rules for drilling apply to beams, joists and blocking, so you are good to go with a few caveats.:
- The hole must be in the centre of the beam (the neutral axis), not toward the top and bottom.
- The hole should not be located close to the ends of the beam.
- The hole shouldn't be directly under a point load.
You probably need a bigger hole for a sink - 2" to 2 1/2" depending on if it serves a kitchen or bath - but that's still within the allowed limits.
2015 IRC R502.8 Cutting, drilling , and notching. See also Figure R502.8
"Holes" are limited to D/3 Max. where D= joist depth and minimum 2 in. from the top and bottom of the joist, or to any other hole located in the member.
The reason for code minimums is occupant safety. I'm just a homeowner/builder/contractor. I see codes as a good thing.
I personally haven't seen a 12x12 in anything under 150 years old, unless a new post and beam.
It just makes me think I would want to find a way around, personally.
Thank you very much for your answers. This is very helpful. Ketith's answer made me wonder about the dimensions of the beam. I had asked my wife to measure the dimensions of the beam but was not specific about what I needed so the 12" included studs nailed along the beam. I went and measured the actual dimensions of the beam and it is more 8" thick by 9 1/2" deep. According to the D/3 max rule, I would still be able to pass a 2" drain pipe (it is a bathroom sink) through.
Thank you for your help.
Louis
Can I assume the support beam in the basement supports a floor above? Wouldn't that mean that there are floor joists resting on the beam. Is there a finished ceiling in the basement? If so, wouldn't there be a 10 -12 inch space between the beam and the floor, with possibly just a piece of blocking that you can either drill through or knock out, in which you can run your 1-1/2 pipe to be above the beam.
If it is actually 5 sistered 2x10's I have a lot less concern than a 200 year old old growth timber.
Keith,
Either way, the wood in the centre of the beam has virtually no forces acting on it unless there is rot.