Can HRV ductwork (insulated of course) be run in an unheated attic space without creating moisture problems?

GBA Editor | Posted in General Questions on

I am building a well insulated/sealed house in Interior BC. I am putting in an HRV and I am wondering where the balance is between simple ductwork design and not going thru the attic space in a cold climate. If I do go thru the attic, the runs will be much simpler than if I go thru my second floor and up the wall (than the ceiling in the bathrooms). Local contractor thinks it will be ok but I am worried about problems in the years to come. Thanks.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Leigh,
    Most HVAC contractors underestimate the importance of duct sealing and duct insulation.

    Ducts installed in unconditioned attics face the worst possible conditions. Your idea can work, as long as:

    1. Every duct joint is impeccably sealed to prevent leakage.

    2. The ducts are insulated to at least R-8. More insulation is always better; you may want to bury the ducts in spray foam insulation or cellulose.

  2. Robert Riversong | | #2

    Another option is to build down the second floor ceiling, or build soffits, to keep the ductwork inside the thermal envelope. No problems, no worries.