Does building code require that we put a sill sealer or capilary break when framing walls on concrete (in a basement for example)?

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Anonymous,
    This is what the IRC requires in section R319.1: "Protection from decay shall be provided in the following locations by the use of naturally durable wood or wood that is preservative treated in accordance with AWPA U1...: ...Sills and sleepers on a concrete or masonry slab that is in direct contact with the ground unless separated from such slab by an impervious moisture barrier."

  2. Peter Yost | | #2

    Note in Martin's response that the code says, "...in direct contact..." If you use a closed-cell foam sill sealer, then the wood and concrete are NOT in direct contact with each other. But you may have to work pretty hard with your building inspector on this one.