Hello GBA,
During the course of a BPI-sanctioned weatherization job, we have come across a newer atmospherically drafting steam boiler boiler that is suffering from a very slight, nuisance level of spilling flue gases. Spillage lasts for about 2 minutes then stops once the stack really heats up. Depressurization is not the problem, nor is a chimney blockage. I believe it is the manufactured configuration of the draft hood.
The solution to this problem seems to be a draft-inducer near the chimney. Anybody having luck with this type of installation? Any other thoughts on how to alleviate a small amount of spillage in order to adhere to BPI standards?
Thanks!
-Arthur
Art, is there another draft hood that would work better? I would talk to either/both the boiler manufacturer or the pipe system manufacturer for advice.