I just had my house, which is near completion, blower door tested with a result of 700 Cfm @ 50p and an ACH of 2.0. This was done with the HRV vents open.
Should I have sealed the vents fot the testing, and would that have made a significant difference?
There are 2 supply vents and 4 exhaust vents.
Thanks for your help.
Bill
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
Yes, intentional openings should be sealed off, and if you had done so you would have gotten lower numbers.
Thanks David. That's what I was afraid of. Care to guess as to how much difference that might have made?
It would probably be very significant. Wild guess... you're getting at least a few hundred CFM50 thru those inlets, and your real number is more like 1.5 ACH50.
If you hired a tester, I might ask why he didn't seal the HRV ports. We did two units yesterday with HRVs and had to go around with a ladder and get all of them.
Bill: Either way, you have nothing to worry about, so get your fishing equipment ready. Whoever built the place did well. j
2 ach 50 is fine in my opinion. vents open or closed. Enjoy your new home. My testers have been reluctant to seal those ports as well. Grrrr.