B&G’s low flow Vario ECM circulator – stupid efficient pumps

fitchplate | Posted in General Questions on

http://bellgossett.com/pumps-circulators/small-circulation-pumps-boosters/ecocirc-heating-auto-and-vario/

What I discovered as a result of the research stimulated by this GBA dialogue is that my circulator controlled hydronic heating will not work with a smart pump like the Alpha, Bumble B or the new Taco model.

You guys understand this but I did not until now. Thermostat controlled circulators turn off when they are not being called upon for heat. That prevents the smart features of the self managed delta-P circulators from doing what they are designed to do. Which in my case, is done instead by my Prestige Excellence boiler.

According to Taco the energy savings of the smart pumps are split 50/50 between reduced electricity demand and more efficient boiler fuel use. Since my boiler’s brain looks after delta-P and delta-T all by itself, I started looking for a circulator that would save the electricity: low flow, variable speed, ECM, manually adjusted pump that could replace my T-stat controlled, 3 speed Grundfos model.

The Magna is a frighteningly expensive pump. Grundfos doesn’t seem to have anything reasonably competitive as far as ECM pumps go. But I ran into Bell and Gossetts Vario. It’s a stupid pump but has an ECM motor with variable speed setting that tops out at 60 watts full throttle. Its closer to the $250 range, unlike G-fos’s stupid ECM pumps that many hundreds of dollars more. So $200 per unit seems pretty good for electricity savings from the ECM side of the modern efficient circulator opportunity.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. user-2890856 | | #1

    Flitch ,
    Could you please attach the I & O Manual for the boiler you are using ? Don't get upset yet . Pressure regulated pumps as I have said before are more for a high head , low flow condition . Delta T pumps will insure that at changing conditions the system will react to the reservoir optimally at all conditions . Your home's system was designed for one outdoor temp and one indoor temp , that only happens for 9 minutes a year . The Delta T ECM circs will make sure that the required energy is being delivered at all conditions as they happen in real time . Delta P pumps only change their rates based on pressure so if you are zoning with thermostats and circs they will do you no good as I have stated before in another thread . The Delta T pump however will work and change it's usage and output in either scenario . You can benefit form Delta T pumping in either case .
    I will contact Taco and get a response which I will post for you to verify what I am saying .

  2. user-2890856 | | #2

    It doesn't work any different with a mod con or a standard cast iron boiler . It just makes sure that the system operates as designed and delivers the energy you have paid to convert . This saves fuel , money and energy .

  3. user-2890856 | | #3

    Maybe I can help you both .

    When a zone turns on the difference between the system fluid and the reservoir (room air ) is at the greatest margin . Maybe right at that moment in time you need 2 gpm , but as the Delta between system fluid and reservoir narrows it cannot shed the energy at the same rate , lower delta , less heat transfer . Moving BTus back to the source that should have been delivered is waste . The Delta T pump recognizes this due to sensors on the Supply and return and slows the flow so that energy is not being wasted and the source can operate as designed .

  4. charlie_sullivan | | #4

    The Grundfos Alpha ECM circulator seems to be running $175 or $146 on Google Shopping, unless you buy the stainless model that's over $300. So I'm not sure why you say it is much more expensive than the $200 B&G.

    The delta-T mode is good for many applications. I wish Bumblebee had a way to set the delta-T target--20 F is too much for a heat-pump system where you only want to run 100 F water.

  5. user-2890856 | | #5

    Charlie ,
    the Bumble bee does have an adjustable Delta T programming function . default is 20* but that can be changed . Just find the directions in the manual . It is adjustable from 5* thru 50* I believe . What kind of system / emitters do you have ?

  6. fitchplate | | #6

    Rich ... I think I got it. The B & G Vario is a delta T pump for circ controlled zones like I have. Here is the boiler manual:

    http://www.triangletube.com/documents/34/PRestige_Excellence_Manual_Part_1_2.pdf

    I an get the Vario through a plumber for $175/ea.

  7. user-2890856 | | #7

    I don't believe the Vario is Delta T technology Flitch but I will verify . It will be a Delta T pump only at absolute design conditions and at no other time . Correct , the Vario is a proportional pressure controlled circ . You will only have a proportional system should you decide to use the TRVs because some will be open and some will be closed or all open , all closed . With thermostats you will never have variation (vario) in pressure . Think about this , if pressure had anything to do with heating systems other than being a measure of what you must overcome at highest flow why does the Universal Hydronics Formula not address it . GPM = BTU divided by Delta T x 500 ? Pretty good question huh ? I can have Bumble Bees shipped to your door for less than the Vario , I will confirm tomorrow and dependent on your location the new VT2218 if you are in New England . It will be available nationwide first quarter . Do not forget about the 100.00 rebate available through many programs when you purchase and buy an ECM circ . Now the things cost about the same as simple PSC pumps after rebate .

    http://bellgossett.com/pumps-circulators/small-circulation-pumps-boosters/ecocirc-heating-auto-and-vario/

  8. wjrobinson | | #8

    ECMs run on less watts per pumped gallon even if not fully taken advantage of They can be set up many ways. Delta P use you would circulate with one circulator feeding zone valves or as in Europe room radiant panels with added tstat valves. Alpha is $156.

    Bumble bee is $210 and is a bit different. I too need assistance figuring how to use it with a modcon. They can work great with a condensing HTP tank water heater.

  9. charlie_sullivan | | #9

    Richard,

    Thanks for correcting my misunderstanding of the Taco Bumblebee/Viridian delta-T capabilities! Being able to go down to 5 F makes that much more appropriate for low-temperature water. From comparing the data, it looks like the Grundfos Alpha is a little more efficient at pumping at a given flow and head, but only a little, and the delta-T mode might help by avoiding pumping faster than necessary.

    In delta-T mode, when the thermostat first cycles on, will the pump go to full speed until it sees the return temperature come up to get the right delta-T? Or will it run at the same speed it found to work well on the last cycle? I could see advantages and drawbacks in either case.

    To answer your question, my house uses ordinary Myson panel radiators with low-temperature water from a GSHP.

  10. fitchplate | | #10

    Apologies, the Vario is not Delta T, it is a variable speed pump with an ECM drive.

    My system being circ controlled with a smart boiler, I understand I can potentially benefit from:

    1. Electricity savings of ECM's
    2. Variable speed - if manual, then settings can be optimized but not self-adjusting

    The question is, can a Delta T auto adjusting circ (i.e Taco D-T) can exceed the advantages of the ECM/ manual variable speed circ, and be compatible with my TT boiler (which is smart in its own right).

  11. user-2890856 | | #11

    Charlie , How low are the temps you are using and do you have TRVs and bypasses on the rads ? Even more important is how the entire system is piped . Please see the Buderus (generic) manual below to determine . Also see the temp and Delta T charts to see how flow and temp effect system . With very low water temps the rads will need to be oversized and the math done to insure they achieve output in any given room , at high temps 194* & 176* you would run a 36*F Delta T and again at 158* & 140* you would run an 18* Delta to maximize heat transfer and efficiency . Pretty close to 20 & 40 . With lower water temps you would have to do the math . calculations for such an equation are explained in this manual and may or may not work with the Mysons but if memory serves me correctly Myson has a very detailed manual also , Buderus' manual however is more plain to see the effects in numbers . The Delta T pump in any case does the same thing as a proportional pressure pump with the exception that it varies flows based on Delta T and since we see Delta T in everybodys manuals and the Universal Hydronics formula you can bet it's more important than pressure . pressure pumps were developed for the European market where in the 40's 7 50's many homes left standing were getting their first central heating systems and small diameter tubing had to be snaked thrpough walls like wire , thus the high head low flow characteristic . Make sense ? You should join th eTaco FloPro neighborhood Charlie and scroll down on the right and locate the circulator webinars and view , also the FloPro University is one of the best tools I find for younger guys coming into my field . Lots of information , presented in a fun manner by one of the best Hydronics teachers on the face of the Earth , plain and simple .

    Flitch ,

    Your boiler will not control Delta T , it will sense high return water temps and shut off on limit . I will look at the manual tomorrow and be able to tell you more . Any heating system can perform better and closer to as designed for conditions while using a Delta T pump . Again , We design the emitters , piping system and size the circs based on Delta T , all of the calculations use Delta T in the equations . Think of it this way Delta T is the answer to an equation , it is simply how much energy was delivered , you deliver more energy to the space with a 20* Delta T than a 10* Delta T with the same flow . You can deliver the same energy at 10 as 20 by doubling the flow , but this would require the circ to use more energy . Wire to water efficiency is also a design concern .

  12. wjrobinson | | #12

    Richard, the Budures PDF explains well radiant panels. But is it outdated in that it does not show using a delta T or P ECM instead of say a bypass valve, which it explains saves the circulator from being dead headed? Seems so.

    My wish is that the emitter and modcon and set back control and ECM variable speed companies would all publish how to use all together. I find no source from the manufacturers of all the parts well integrated in designs and up to date to what is available now and in 2015.

    Working on having some set systems ready to go.
    Phoenix
    Bumble Bee
    radiant panels
    and less parts.
    -for hot water, hydronic heat.
    1000-5000sqft installs.

    I will be calling some day and see what we can put together. Especially for my current system update which is not happening till I close the camp for the season.

  13. user-2890856 | | #13

    I will be available to discuss when you are ready AJ . You have my contact information . I know very well how to do what you are talking about
    The Buderus manual is awesome and shows how to do the math to make the emitters work properly through a variety of conditions . Also shows how the Delta between the room and the emitter effect output and performance .

  14. wjrobinson | | #14

    Richard I agree the pamphlet is super for some knowledge but it shows too many piping systems and also does not show a piping system with a Delta T single circ. to zone valves along with radiant panels with a condensing water holding boiler like a Phoenix. Post a drawing example of what you would do. Would you just simply use the Bumble Bee in one of their shown diagrams? That's what I am thinking. I know one thing not many homes my way have radiant panels but more and more do. Same with mini splits, if you talk mini split all anyone around here says is, " yes installed those AC units for years now, where have you been? Then ask them about heating with them and you get a blank stare.

    When I installed my radiant floor system back in '92 no supply houses were set up selling into that market. Online info and ordering for years. Still rare here. Modcons are going in, but I believe they are not being used right most of the time. 180 degree loops are not for modcons. Over sizing radiant panels is the one way that does work. Radiant floors is another. You're the expert, correct my mistakes gladly accepted and desired.
    aj

    Right now working on a small existing renovation project, 1000sqft of radiant staple up , in 3 3/4" 12" OC spaced loops, 500sqft second floor standard 25' baseboard loop. 3 circulators for zones, one circulator for primary, 93,000 IBR low mass boiler. System has worked for 2 decades, is being redone soon. The radiant floor has to stay due to the crawlspace situation, so that part is not changing though I am going to add zones as rooms that are heated most of the time has changed with time. Also would like lower the head per loop.

    If I can work some magic with redoing this system, I will be a happy camper for 2015. When I shut it down I can give you specifics.

  15. user-2890856 | | #15

    AJ ,

    I'd be glad to help you . Contact me to discuss and send a room by room heat load calc . I will assist you in the design but will not post drawings here as they are proprietary and for sale . My time is too valuable to justify to these folks what I do . I will certainly help you out though .
    I just helped Flitch solve his issue privately and extend the same to you .

  16. wjrobinson | | #16

    January shut down coming. Will have my existing system detailed and emailed.

    I just hurt my brain reading this at heating help...

    http://forum.heatinghelp.com/discussion/150143/delta-p-vs-delta-t

  17. user-2890856 | | #17

    You should check this one out , some heavy hitters took part in this one .
    http://forum.heatinghelp.com/discussion/151689/the-recent-boiler-talk-episode

  18. fitchplate | | #18

    Yes, thanks Rich, for your help. I am poised on the brink of ordering 4 Viridians (VT1128) -- (which you exposed me to in the first place, AJ) -- to enable Delta T management on my circ controlled zones. (No zone control valves in my hydronics).

    http://flopro.taco-hvac.com/media/Viridian_VT2218_100-114.pdf

    I will be replacing my 3 speed Grundfos pumps. This system has T-stats so these pumps are shut off when flow is not being called for. The Viridians are manually set so there is no risk of losing settings from the T-stat shut off like there would be on the Delta P circs (i.e. you can’t turn them on and off) which probably would not work on my low flow homerun panel rads anyway… according to the FloPro team blog at Taco.

    Also, according to some of those “heavy hitters” on Heating Help (better known as the The Wall) the Delta P's may conflict with smart modcon’s low mass boilers’ PID coordination.

    http://tekmarcontrols.com/support/tekmarglossary/33-support/glossary/200-zone-load-coordination.html

    (Rich, please correct me if I make yet another mistake). According to Taco techies, with my set up (combi boiler with DHW priority and internal buffer tank), I have a primary/secondary format so the boiler’s brain works the primary loop (with its own circulator) while the zone controlling circs are working the secondary piping where I have my manifolds supplying the European panel rads. This makes intuitive sense to me but I didn’t have the language for it myself. You can imagine the PID control flow control variables from the illustration.

    http://flopro.taco-hvac.com/deltat_resources.html

    These panel rads are so sweet at low flow; they don’t blast heat like old style and high temp rads; they make the place very cozy all the way around. And there are no forced air stratifying heat pump mini splits allowed in my place. And hopefully the ECM plus Delta-T features of the Viridians will save me electricity and propane.

  19. wjrobinson | | #19

    Flitch your total head is high I take it so you need that circ?

    I too have either to redesign my loops to less head which I plan on doing or I too would need a circ for higher head than the bumble bee puts out.

  20. fitchplate | | #20

    AJ, I did not understand that the Viridian was recommend for my situation due to higher head, although I guess panel rads have more head than fin tube etc.

    My understanding is that the Viridian is replacing the Bumble Bee, not adding to the line. I understood it to be the better choice (over the BB) as it would a better job of (1) regulating and optimizing the Delta T and (2) slowing the flow for better emitter performance. How does that sync with a high head condition?

  21. user-2890856 | | #21

    Flitch ,

    Don't put the cart ahead of the horse . You very well not have what we could call high head because of the way you are piped . Manifolds with homeruns to each rad hardly makes high head a certainty . I will know for sure after seeing the calcs you have . Unless you just wanna tell me the lengths from boiler to manifold , manifold to panel rad and what size the rads are . You only need be concerned with the highest head circuit , that's the one that is in charge , all the flows must be added together however .

  22. user-2890856 | | #22

    Flitch and AJ ,

    Read these . Basically all you could want to know . I like the Delta T dawn blog personally . LMAO

    http://flopro.taco-hvac.com/images/Delta-Tblogs.pdf

  23. wjrobinson | | #23

    Head is 16 verses 22 for the two circs we are discussing, if you look at the pump charts Flitch.

  24. user-2890856 | | #24

    What pumps are you looking at AJ ?

  25. kevin_in_denver | | #25

    Flitch,

    You said "correct me if I'm wrong". Then you said " there are no forced air stratifying heat pump mini splits allowed in my place. "

    In a well insulated, draft-free house, the stratification is insignificant. It doesn't matter if there is a blower or not.

    But you are right if you are trying to say that a drafty, poorly insulated house heated hydronically will usually have less stratification than the same house heated with a natural gas furnace.

  26. wjrobinson | | #26

    Rich the head charts for a Bumblebee verses the Viridian that Flitch mentioned. Not for me, I was commenting as to Flitch's pump choice and wondering why he had to go for the pump with higher head.

  27. user-2890856 | | #27

    AJ,

    You'll notice that the VT2218 also will go lower on the x & Y axises also . I think that is more the concern in modern , tight buildings .

    Kevin , air movement and any current in ANY house will allow your body heat to be lost . Think along the lines more of not heating a house but allowing humans to shed or hold onto their body heat dependent on season .
    The latest thought that there is a cheap mechanical solution to comfort troubles me . Are we trying to save the planet or the planet and people . I cannot post this enough , Indoor environmental quality always trumps indoor air quality but it also addresses it . The occupants are the most important thing after all .