Best approach to air sealing existing outlets?

dave_naff | Posted in General Questions on

Currently engaged in an energy efficiency upgrade. We have largely figured out most of the air barrier and sealed with a mix of membrane (Henry Blueskin), tapes+liquids (Tescon and Visconn), and even a little caulk and spray foam here and there. 

That said, there are some areas where we can’t easily access the top plate and our early blower door test showed leakage through the outlets and switches on the walls with the unsealed top plate.

My current thinking is to try and seal those drywall penetrations, effectively making the top floor drywall on those faces the relevant air barrier.  

What’s the best approach for air sealing existing outlets? 

It seems the gaskets don’t do a great job. I can obviously easily apply caulk around the gap between the outlet and the drywall, but that still leaves the knockouts and wire penetrations unsealed.

Is there such a thing as an airtight outlet & cover?

Thanks in advance!

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. freyr_design | | #1

    I think you are going to have to air seal the boxes themselves. Though I will point out that, when you air seal just this wall, you still have communication with other walls in your house as the wires run between walls, so I don't think just air sealing at drywall on this wall is going to do anything. You will get air from all your other walls using this wall top plate penetrations. If you are really concerned with it you could always rip the drywall just below your top plate in a strip and air seal there. Idk if thats worth it but would probably be the easiest way if you can't access from above.

    1. dave_naff | | #7

      Yeah, we actually contemplated exactly this. I came out with the view that it isn't probably worth it to do all the drywall cuts...

      I'm hoping for something like the airtight led recessed light replacements. As long as you can get a good seal around the light, they should theoretically be airtight.

      Any idea on the air tightness of the tamper resistant outlets?

      1. freyr_design | | #8

        No sure about the tamper proof, I do think you could get a fairly good seal on the box from the inside using a tape like tescon vana and some origami skills. I found it to one of the better ways to air seal boxes. Foam I found just breaks when wires wiggle in the slightest and caulk and putty can be messy, especially on the inside I would be a little worried about it. The tape is low profile an tolerates wire movement.

  2. user-5946022 | | #2

    Yes, they make airtight outlet boxes. There are a variety of brands, but vapor seal is one:
    https://alliedmoulded.com/product/two-gang-electrical-box-for-use-with-nonmetallic-sheathed-cable-2302-nkv/

    Another option is to apply putty pads, typically used for fireproofing, to the backside of the box after the wires are run.

    Another option is these cardboard things that you then spray one part canned foam between the cardboard boxes and the J box.

    If the space is finished you can seal the boxes with an extra long tip on a caulk tube.

    1. freyr_design | | #3

      That is not an outlet, it is a junction box

      1. user-5946022 | | #10

        Thanks. Fixed. I was tired.

    2. dave_naff | | #5

      These are all great products. Unfortunately I'm trying to solve a different problem: that of an existing outlet already behind a wall...

      I'd prefer not to open the walls to seal the backs of the outlets...

      I guess the question is can I use firestop caulk (or putty) from the inside of the outlet?

      1. user-5946022 | | #9

        If the space is finished, you can seal the locations in the boxes where the wires penetrate the box, and the random holes in the box with an extra long tip on a caulk tube.

        Most of the air leakage is usually between the drywall and the box, so I'd start by removing the plates and sealing that gap.

      2. stamant | | #13

        can you put material inside of the box? sure.
        is it a good idea? no

        just guessing but NEC likely doesn't want anything foreign inside of the box.

        the # of conductors allowed inside of a box is dictated by the quantity and size of the wire and number of devices. seems sketchy to estimate how much box fill volume would be diminished.

        practically it's really hard to seal around wires or sheathing. conductors move when you stuff receptacles or switches back inside the box.

        drywall layer isn't sealed at the floor either so stripping the drywall at the top means stripping the baseboard at the floor too.

  3. matthew25 | | #4

    Duct seal putty has been recommended in the past for exterior wall outlets. It is pretty malleable and can wrap around where the wires enter the box. Your situation is a lot tougher since drywall is already installed. Blower door directed air sealing should have happened while you still had access to everything.

    1. dave_naff | | #6

      Well, the house was built in 1930 and last remodeled in 1990. The walls in question weren't opened with this current project. We did do a mid-project blower door test and did see some air leakage through these outlets, hence my desire to seal them. As I understand it, putty on the inside of the box is a no-go right?

      1. user-5946022 | | #11

        You typically don't want to use up any of the space in the box as there is a min amount of free space needed for wires & outlets, etc.
        You also don't want anything flammable inside the box.
        That is why caulking with an extra long nozzle works well if you really want to get into the back of the box where the wires come in.
        Otherwise, just remove the plate covers and seal the gap between the box and the drywall. That helps ALOT.

      2. charlie_sullivan | | #14

        If you can meticulously put duct seal putty in the right spots in the back of the box, without adding significant volume, that's fine. Not flammable, not subtracting from the required space, not using a material that's not approved for the purpose. Opinions seem to vary as far as how long it will take to dry up and crack but it will never be worse than without it.

  4. Expert Member
    DCcontrarian | | #12

    I like 3M FB-FOAM for sealing outlets. See https://www.amazon.com/3M-Block-FB-Foam-Orange-Aerosol/dp/B008KNP928/, although it's probably cheaper locally. It's less sticky and easier to shape than most spray foams, so it's easier not to make a mess.