Bath fan exit with 2×4 walls and bird cut rafters. TIGHT!

PAUL KUENN | Posted in Green Building Techniques on

As with my own home (1960 2×4 walls with 2×8 rafters with hip roof), I’ve been asked to add bathroom fans for others. The roof sheathing is only 3.5″ above the top wall plate so I usually go from 4″ rigid round duct (don’t want to lose cfm) to 10″ wide rectangle, extension to get it over wall plate then back to round. I use a butterfly style backdraft damper near the fan so it’s under the insulation. I try to seal it before pushing it through the narrow soffit opening. Not easy when you have zero head room. I need to keep it very narrow where it becomes rectangular because I like to seal above the top plate with 1″ XPS and foam and lay the rectangular duct on top. Usually this is squashed against the underside of the roof sheathing. I did find a manufactured rectangular duct with double angles but it has a backdraft damper which ends up on the cold end which means it will most likely fail when temps are below zero. Anyone out there that has a better idea? Is it just better to exit the roof?
Thanks, PK

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
    BILL WICHERS | | #1

    Are you trying to exhaust the fans under the soffit? This can introduce other problems if it’s a vented soffit since the humid exhaust air is likely to get drawn in to the attic through the soffit vents.

    Here is an article explaining bathroom fan venting:
    https://www.finehomebuilding.com/2018/03/01/bath-fan-venting-cold-climates

    Bill

  2. PAUL KUENN | | #2

    Thanks! Old plywood covered soffit (with retro aluminum placed over wood), next vent is over 10' away so no issue there.

  3. PAUL KUENN | | #3

    I usually vent up out the roof away from street side using 4" PVC pipe. I can keep the run short (again, we're talking about a 4:1 pitch hip roof) and use blanket insulation around the pipe. I use a large 90 degree elbow and 45 for a downslope exit and I've never seen condensation drip back down inside. I use the best butterfly spring damper close to the fan so it's buried under lots of insulation.

  4. seabornman | | #4

    We had a similar situation with leaky bathroom exhaust duct causing ice dams and roof leaks. I threw that system away and put in a through the wall Panasonic unit. Very happy with it.