Basement slab insulation

ColbyForester | Posted in General Questions on

In building a new house at the Alabama/Tennessee State line, Technically Zone 3. Is basement slab insulation needed or recommended for my climate?

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Colby,
    No (unless you are planning on installed PEX tubing in the slab for a hydronic heating system).

    For more information, see this article: "Determining Sub-Slab Rigid Foam Thickness."

  2. Expert Member
    Dana Dorsett | | #2

    Code doesn't demand it, but in humid Zone 3A there may be a rationale for 1-1.5" of EPS under the slab to keep "musty basement smell" at bay during the humid summer when the slab temp could otherwise be well below the ventilation air's dew point, and could still have a lifecycle rationale on energy costs. See Table 2, p.10:

    https://buildingscience.com/sites/default/files/migrate/pdf/BA-1005_High%20R-Value_Walls_Case_Study.pdf