Andrew207 | Posted in General Questions on

I’m going to be blowing in cellulose into my attic. I’ve installed ventilation baffles, but I’m wondering how much cellulose I can add? How much higher does the top of the baffle need to be compared to the level of the loose cellulose? Thanks. -Andrew

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Jon_Harrod | | #1

    Depending on truss design and roof pitch, you can often get to R-60 with a single course of baffles. If you're careful, you can bring the material up within a few inches of the tops. The trick is to minimize the amount of airborne material so that you don't clog the baffles. I like to keep the hose buried so that it gradually pushes the material up from below. Expect 10-15% settling, after which the tops of the baffles will be well clear of the material.

  2. GBA Editor
    Martin Holladay | | #2

    Andrew,
    Baffles are usually inexpensive (although admittedly they can take a while to install). If your baffles are a little short, I would hate to hear that you decided to install less insulation that you wanted, just because of a small error in your baffle height.

    When in doubt, you want to go a little deeper with your insulation. If you are right at the margin, install longer baffles so you can go deep with the cellulose.

  3. Andrew207 | | #3

    I measured the height of the baffles. I can get R60 and still have at least 2 to 3 inches of clearance. Is this adequate clearance? I think I'll also point the hose down into the material like Jon says to minimize future settling.

  4. GBA Editor
    Martin Holladay | | #4

    Andrew,
    It sounds like you are good to go -- as long as you plan for the fact that the cellulose with settle 13% to 15%.

    If you are assuming that you need 16.5 inches of settled cellulose to achieve R-60, you should install 18.5 or 19 inches of cellulose.

    For more information on this topic, see How to Install Cellulose Insulation.