Are tar paper and Tyvek a vapor trap?
Can you please set me straight because I am getting different points of view on this. My home is 40 years old, has the old type of sheathing, a layer of tar paper and then T1 11 siding. In patching one side of the house, I have put 1/2 inch foam board over the T1 11 and then Tyvek. Is this a vapor trap? If so, what part of it is?
Is the use of tar paper and then a layer of Tyvek on the outside of the T1 11 a vapor trap?
Is the use of rigid foam board a vapor trap?
Thanks so much!
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
C.K.,
In most cases, including yours, there are no problems associated with two layers of housewrap (for example, asphalt felt and Tyvek). Both types of WRB are somewhat vapor-permeable. (Asphalt felt is a so-called "smart" vapor retarder with variable permeance.)
A problem might arise, however, from the use of exterior foam -- depending on your climate zone and the type of foam. In your case, a vapor-permeable foam like uncoated EPS would not be a problem; however, a foil-faced foam would be a problem, especially if you live in a cold climate. For more information on this issue, see Calculating the Minimum Thickness of Rigid Foam Sheathing.
Hi,
Thanks for the response. I live in Chicago. Because I was patching areas of my home, I have already put the 1/2 inch Foamular product and then Tvek, both over the existing T1 11. Foamular claims their product has the same permability as OSB board.
I did read that post and am still not sure if I should tear the siding off my house. There are areas that have a plastic vapor barrier on the interior walls, over Roxul (which is what they recommend). If it is definite that I should tear out the Foamular rigid board, I would love to know so I can get that done. Thanks!
C.K. North,
No, you don't have to remove the siding and the 1/2-inch Foamular. Your wall will be OK, as long as you do a good job installing flashing to keep rain out of your wall.