Are tar paper and Tyvek a vapor trap?
![](https://secure.gravatar.com/avatar/63b74bbfad47220822f7f8ceb4d1817b?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fc.png&r=g)
Can you please set me straight because I am getting different points of view on this. My home is 40 years old, has the old type of sheathing, a layer of tar paper and then T1 11 siding. In patching one side of the house, I have put 1/2 inch foam board over the T1 11 and then Tyvek. Is this a vapor trap? If so, what part of it is?
Is the use of tar paper and then a layer of Tyvek on the outside of the T1 11 a vapor trap?
Is the use of rigid foam board a vapor trap?
Thanks so much!
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
![](https://www.greenbuildingadvisor.com/app/themes/greenbuildingadvisor/dist/img/modules/detail-library/thumb1.png)
![](https://www.greenbuildingadvisor.com/app/themes/greenbuildingadvisor/dist/img/modules/detail-library/thumb2.png)
Replies
C.K.,
In most cases, including yours, there are no problems associated with two layers of housewrap (for example, asphalt felt and Tyvek). Both types of WRB are somewhat vapor-permeable. (Asphalt felt is a so-called "smart" vapor retarder with variable permeance.)
A problem might arise, however, from the use of exterior foam -- depending on your climate zone and the type of foam. In your case, a vapor-permeable foam like uncoated EPS would not be a problem; however, a foil-faced foam would be a problem, especially if you live in a cold climate. For more information on this issue, see Calculating the Minimum Thickness of Rigid Foam Sheathing.
Hi,
Thanks for the response. I live in Chicago. Because I was patching areas of my home, I have already put the 1/2 inch Foamular product and then Tvek, both over the existing T1 11. Foamular claims their product has the same permability as OSB board.
I did read that post and am still not sure if I should tear the siding off my house. There are areas that have a plastic vapor barrier on the interior walls, over Roxul (which is what they recommend). If it is definite that I should tear out the Foamular rigid board, I would love to know so I can get that done. Thanks!
C.K. North,
No, you don't have to remove the siding and the 1/2-inch Foamular. Your wall will be OK, as long as you do a good job installing flashing to keep rain out of your wall.